Hi all,

Having a blank moment and wondered if anyone can help!

I have been asked to move a meter from the mains head to about 20m away, i know i cant touch the meter but i need to install the cable to an isolator.

Is there a maximum distance EDF will allow from the mains head?

Cheers :D
 
Not sure what EDF request but most DNO insist that if you extend tails over 3 metres then you should run in either SWA or Concentric.

Also that there should be a protection device installed to protect the cable. If the run is surface then you can use a standard switch fuse, if the cable falls under regs 522.6.5 or 522.6.6 then it has to be RCD or RCBO protected.
 
Hi all,

Having a blank moment and wondered if anyone can help!

I have been asked to move a meter from the mains head to about 20m away, i know i cant touch the meter but i need to install the cable to an isolator.

Is there a maximum distance EDF will allow from the mains head?

Cheers :D

Just wondering Matty who asked you this? I've had many jobs moving the CU but not sure a DNO will want it's meter 20meters from the header
 
Just before you go down the road of thinking about costing or anything ...............make sure the DNO will do this, as I said they aren't to happy about seperating headers and meters ..................think they are afraid they might get lonely without each other ;)
 

Reply to Metering info in the Australia area at ElectriciansForums.net

Similar Threads

Client has had a meter installed for a new consumer unit in their shop they are looking to rent out the spare space for a barber shop so they want...
Replies
10
Views
434
Morning all, Really hoping to get some advice / confirm what a few of us are thinking about a job in the future. Back ground - We have to swap...
Replies
15
Views
478
Hi there, I built a house with ground source heating 5 years ago and it's a fairly large house so I have 3 phase supply 80 amps per phase. I had...
Replies
7
Views
1K
Hi, need some advice, I moved over from Sse in 2020 to Octpus energy. Whilst I was with SSE I was on E10 when I went over to octopus they put me...
Replies
1
Views
484
We have a meter EDMI - ES30B fitted to our property. I understand from the fact sheet for the smart meter...
Replies
13
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock