Agree with all above... getting a new rcd/rcbo board roughly the same height will be an easy enough change. Looks like all the MICC is surface clipped, so can get a bit of play on the cables.
Doesnt even need the ends reterminated, if care is taken removing the old board.

Other option, although might look rough... is to use this old board as a joint box and mount the new board directly on top, passing the cables through the rear of the new board.
 
One unlikely but technically possible scenario that should be mentioned: If the original installation work was done hastily, and has not since been tested, there is a small possibility of finding leaky seals on the MICC that have allowed moisture to enter the cable over time. In some cases that can be remedied, but would depend on a lot of specifics that are hard to judge at a distance. In principle, MICC is a very reliable and durable cable system, but I have been caught out once with a system that had a large number of breathing seals, perhaps because one member of the installation team was inexpert or slipshod. The system worked perfectly for many decades but I could not give it a satisfactory EICR due to the compromised insulation resistance.
 
I noticed the termination is bushed straight onto the CU nothing wrong with that, I just always preferred to also use coupler and bush less strain on the pot for all of my terms.
 