Hi people,

I'm having a brain fart moment. What is the minimum distance between enclosures, with doors that are facing each other?

In EN60204-1:2006+A1:2009 section 11.5 said " In the case where such parts are present on both sides on the access way, the clear width shall be at least 1.5 m."
In EN60204-1:2018 section 11.5 has removed the dimensions for between cabinets. Not sure why.

Ok, so the only dimensions I can find now between enclosures are in BS7671 section 729. Operating And maintenance Gangways. Which says 700mm.

So, my question is, am I missing something? Is there any other reg I'm missed, or are we just going with a distance of 700mm now?
 
700mm doesn't seem right.
Is that with a panel either side or just a gangway with a panel at the end?

Maybe there have been revised studies done on the how bodies behave / fall when thrown out of a panel after an electric shock
The original rule of thumb for access space to a panel used to be far enough so that if you are thrown (blown) away from the panel you wouldn't hit a surface behind you and bounce back into it, now incapacitated.
With a panel either side it would need to be more to stop you being thrown into an open panel behind you.
1.5mtr would seem to be the minimum regardless of any regs.
 
700mm doesn't seem right.
Is that with a panel either side or just a gangway with a panel at the end?

Maybe there have been revised studies done on the how bodies behave / fall when thrown out of a panel after an electric shock
The original rule of thumb for access space to a panel used to be far enough so that if you are thrown (blown) away from the panel you wouldn't hit a surface behind you and bounce back into it, now incapacitated.
With a panel either side it would need to be more to stop you being thrown into an open panel behind you.
1.5mtr would seem to be the minimum regardless of any regs.

I agree, but they have taken that distance from EN60204. Not sure why they have taken this from the reg.
Now looking for some reg that states a distance and all I can find is in BS7671, which states 700mm.
My boss was asking as they are shifting some cabinets on a site. No one can find a distance other than the 700mm. (We are not going that close)
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Spoon

Mentor
Arms
-
Joined
Location
Lancashire
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Electrical Engineer (Qualified)

Thread Information

Title
Minimum distance between electrical enclosures
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
3
Unsolved
--

Advert

Thread statistics

Created
Spoon,
Last reply from
Spoon,
Replies
3
Views
6,716

Advert

Back
Top