I think I may have asked this question a while ago but not sure on what the answer was and it's come up again at our monthly tool box talk.

When doing a Minor works for an additional spurred socket or extra light fitting on a circuit, should the R1+R2 measurement be taken from the protective device or the socket/fitting you have spurred from?
 
Why would you be recording the R1+R2?
What is the purpose behind it?
You nee to ensure that the circuit you are adding, altering etc is correct, if the RFC you are adding a spur to, and the R1+R2 was suspect, indicating that maybe it is not wired correctly, then adding a new spur may not be the best option, that's how I read it Spin.
 
18th Ed MWC asks for continuity readings as well as Zs.
Agree Mate, but the question the OP posed, or at least I think this what he is asking, is would you need to take continuity readings of just the new cable installed, or the continuity of the new and existing circuit, my thoughts are post 6.
 
You nee to ensure that the circuit you are adding, altering etc is correct, if the RFC you are adding a spur to, and the R1+R2 was suspect, indicating that maybe it is not wired correctly, then adding a new spur may not be the best option, that's how I read it Spin.

I think Spin knows the answer but is trying to help the Trainee.
 
but it's not just the form, it's to confirm that there is a cpc to each point
 

Reply to Minor works R1+R2 measurement in the Electrician Courses : Electrical Quals area at ElectriciansForums.net

Similar Threads

  • Question
Hi there, I’m a new member to the forum and felt like I could do with some additional insight into a fault I came across on a call-out at the...
Replies
6
Views
405
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Hi everyone, I’m brand new to the site and hope everyone is doing well. My question is this: I have a 2365 level 2 diploma and have been doing...
Replies
6
Views
1K
Hey there, Sorry I’ve just joined up. I’m a qualified electrician/Electrical engineer. Recently sat my 2391-52. My question is I had a fault...
Replies
4
Views
1K
Hi, can someone give me some advice RE completing a small works certificate for a fused spur coming from a ring final. 1) In part 2 of the AMD2...
Replies
35
Views
7K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock