L
loz2754
On the question of which regulation states that you cannot use a CPC from one circuit to add a CPC to a different circuit, you will not find any such regulation. On the contrary 543.1.2 and onward shows the requirements for where two or more circuits share the same CPC. So in some circumstances it might be perfectly acceptable.
However, as Lucien and others have pointed out, this would not be an appropriate solution to the "missing" CPC in your situation. You would only be masking the symptoms, not correcting the fault.
A bit like taking painkillers to treat a bleeding artery. You need to find the problem and repair it.
However, as Lucien and others have pointed out, this would not be an appropriate solution to the "missing" CPC in your situation. You would only be masking the symptoms, not correcting the fault.
A bit like taking painkillers to treat a bleeding artery. You need to find the problem and repair it.