Was informed of this incident last week. A row of period houses in an older part of the city. All on TT earthing. One gets rewired. TNCS is obligatory for all new installations. DNO suffers a neutral break close to the trafo. All 23 houses now divert their neutral current back through the neutralised houses main (and supplementary) bonding. As it was an older part of town the metallic services were all intact and provided a low resistance path back to the trafo. It was estimated this home had up to 700 amps travelling through it at one point. Though no fire occurred there was massive smoke damage resulting in huge damage.

Two lessons for me.
.1) Check the neighbours supply system when doing rewires.
2) Consider electrically isolating any main metallic services still in use
 
Took me a few mins to work that one out but yeah I can see how the other houses have no path back as the earth is completely separate, however one house has neutral an earth combined so all the current tries to go back via that earth connection..

Is it obligatory to change from TT to TNCS?

I have found that the metallic services provide a lower resistance to earth than the earth rod although would that not have made it worse as the earth rod would still be the only path back to the transformer?

I wonder if we will ever get to a point where it will be mandatory to fit a device that will detect a PEN fault, we now have them, why not install one at incomer, probably a better safety feature than an SPD?
 
Interested but don't know much about this


For the 23 houses would that not be fed from a 3P trafo and the neutral current would be the vector sum so 700 seems high ?

Had a few beers could be talking rubbish


How does the pen fault detector work on an incommer then ?
 
Last edited:
I thought the ROI now mandated double-pole MCB as the main incomer switch, so I presume the 'neutralising link' is at the supply head, and not in the CU?

I think the Americans have a N-E link in the CU but I don't know if it is before or after the incoming isolator. If it were on the isolated side a DP MCB would have cut out the fault fairly fast!
 
We only have a reliable solution if all 3 phases are present

the current signle phase options are not really a solution

I think the DNOs should implement PEN fault disconnection as they have access to all phases easily, but that would require more cost

Don't some EV car chargers have PEN fault detection? I think there is also a standalone system that can detect PEN fault..

I cant see any DNO ever implementing a PEN fault disconnection as that would cost them money, I think the next edition of wiring regs will have all sorts of fancy earthing because the DNO's no longer want to provide a reliable earth so cant see them will to accept responsibility to disconnect a PEN fault.
 
Can you show a link of where it says you have to have a TNCS if doing a rewire... First I have every heard of this...
The DNO (ESB) will only provide you with a TNCS supply. On coming across a TT supply, a REC (registered electrical contractor) is obliged to issue a "Notice of Hazard" to the homeowner, alerting them of the requirement to upgrade to TNCS. No exceptions are allowed.
On the most recent "Safe Electric" newsletter, they doubled down on this by stating that metal sheds may not be connected to a converted TT supply (see March 2021 newsletter under "faq, s" on page 12, I think).
 
The DNO (ESB) will only provide you with a TNCS supply. On coming across a TT supply, a REC (registered electrical contractor) is obliged to issue a "Notice of Hazard" to the homeowner, alerting them of the requirement to upgrade to TNCS. No exceptions are allowed.
On the most recent "Safe Electric" newsletter, they doubled down on this by stating that metal sheds may not be connected to a converted TT supply (see March 2021 newsletter under "faq, s" on page 12, I think).

Agh ok your in Ireland....
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

LastManOnline

Arms
Supporter
Joined
Location
Ireland
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
Ireland
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)
Business Name
Able Electrical

Thread Information

Title
Mixing TT and TNCS supply systems
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
25
Unsolved
--

Advert

Thread statistics

Created
LastManOnline,
Last reply from
Mikegh,
Replies
25
Views
6,954

Advert

Back
Top