We only have a reliable solution if all 3 phases are present

the current signle phase options are not really a solution

I think the DNOs should implement PEN fault disconnection as they have access to all phases easily, but that would require more cost

Don't some EV car chargers have PEN fault detection? I think there is also a standalone system that can detect PEN fault..

I cant see any DNO ever implementing a PEN fault disconnection as that would cost them money, I think the next edition of wiring regs will have all sorts of fancy earthing because the DNO's no longer want to provide a reliable earth so cant see them will to accept responsibility to disconnect a PEN fault.
 
Can you show a link of where it says you have to have a TNCS if doing a rewire... First I have every heard of this...
The DNO (ESB) will only provide you with a TNCS supply. On coming across a TT supply, a REC (registered electrical contractor) is obliged to issue a "Notice of Hazard" to the homeowner, alerting them of the requirement to upgrade to TNCS. No exceptions are allowed.
On the most recent "Safe Electric" newsletter, they doubled down on this by stating that metal sheds may not be connected to a converted TT supply (see March 2021 newsletter under "faq, s" on page 12, I think).
 
The DNO (ESB) will only provide you with a TNCS supply. On coming across a TT supply, a REC (registered electrical contractor) is obliged to issue a "Notice of Hazard" to the homeowner, alerting them of the requirement to upgrade to TNCS. No exceptions are allowed.
On the most recent "Safe Electric" newsletter, they doubled down on this by stating that metal sheds may not be connected to a converted TT supply (see March 2021 newsletter under "faq, s" on page 12, I think).

Agh ok your in Ireland....
 
On coming across a TT supply, a REC (registered electrical contractor) is obliged to issue a "Notice of Hazard" to the homeowner, alerting them of the requirement to upgrade to TNCS. No exceptions are allowed.
Has the nature of the hazard been described?

Is it this very issue of TT'd homes returning open PEN current via another's neutralising link?
 
Has the nature of the hazard been described?
The description of the hazard would simply be termed as the home being "un-neutralised".
Is it this very issue of TT'd homes returning open PEN current via another's neutralising link?
Yes. That's one issue. But main issue is the gradual disappearance of the metallic network that was deemed essential for a sustainable TT system.
 
These systems only disconnect the supply if the L - N voltage is outside of range of 207v - 253v it is still very possible to have a PEN fault with a dangerous voltage present on all exposed metal work and these devices would be non the wiser, therefore they do not protection against PEN faults in everycase

Other products have a device which senses any current flowing on the CPC, these require a person or animal to receive a shock for a very short duration in order for them to disconnect in a PEN fault scenario

So as yet we do not really have a satisfactory single phase PEN fault detection/protection device
 
These systems only disconnect the supply if the L - N voltage is outside of range of 207v - 253v it is still very possible to have a PEN fault with a dangerous voltage present on all exposed metal work and these devices would be non the wiser, therefore they do not protection against PEN faults in everycase

Other products have a device which senses any current flowing on the CPC, these require a person or animal to receive a shock for a very short duration in order for them to disconnect in a PEN fault scenario

So as yet we do not really have a satisfactory single phase PEN fault detection/protection device
A protective device that requires a person to receive a shock

Hmm


Not sure I like the sound of that
 

Reply to Mixing TT and TNCS supply systems in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Carrying out a EICR in a commercial setting. In the main intake room the DNO supply comes in and it states clearly this is a PME system. 5 years...
Replies
5
Views
1K
Doing a lot of EICRs at the moment and have came across what I'm sure is a common enough problem. In an off grid rural cottage I have a TT system...
Replies
20
Views
3K
TNC-S main supply with 16mm swa supplying garage consumer unit from main consumer unit in house, then 4mm swa supplying pond equipment through...
Replies
36
Views
3K
Hi guys I was recently ask by a customer if/how his house could be supplied by his electric car. He wants to charge the car at night on low rate...
Replies
4
Views
1K
As the title says, I am looking for a recommendation for an enclosure and gland arrangement to electrically isolate or divorce the earth/armouring...
Replies
25
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock