Was informed of this incident last week. A row of period houses in an older part of the city. All on TT earthing. One gets rewired. TNCS is obligatory for all new installations. DNO suffers a neutral break close to the trafo. All 23 houses now divert their neutral current back through the neutralised houses main (and supplementary) bonding. As it was an older part of town the metallic services were all intact and provided a low resistance path back to the trafo. It was estimated this home had up to 700 amps travelling through it at one point. Though no fire occurred there was massive smoke damage resulting in huge damage.

Two lessons for me.
.1) Check the neighbours supply system when doing rewires.
2) Consider electrically isolating any main metallic services still in use
 
Well that's interesting

Do the DNO not have any rules on mixing supply types

You would think it would be down to them to ensure this doesn't happen
 
Took me a few mins to work that one out but yeah I can see how the other houses have no path back as the earth is completely separate, however one house has neutral an earth combined so all the current tries to go back via that earth connection..

Is it obligatory to change from TT to TNCS?

I have found that the metallic services provide a lower resistance to earth than the earth rod although would that not have made it worse as the earth rod would still be the only path back to the transformer?

I wonder if we will ever get to a point where it will be mandatory to fit a device that will detect a PEN fault, we now have them, why not install one at incomer, probably a better safety feature than an SPD?
 
Interested but don't know much about this


For the 23 houses would that not be fed from a 3P trafo and the neutral current would be the vector sum so 700 seems high ?

Had a few beers could be talking rubbish


How does the pen fault detector work on an incommer then ?
 
Last edited:
I thought the ROI now mandated double-pole MCB as the main incomer switch, so I presume the 'neutralising link' is at the supply head, and not in the CU?

I think the Americans have a N-E link in the CU but I don't know if it is before or after the incoming isolator. If it were on the isolated side a DP MCB would have cut out the fault fairly fast!
 

Reply to Mixing TT and TNCS supply systems in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Carrying out a EICR in a commercial setting. In the main intake room the DNO supply comes in and it states clearly this is a PME system. 5 years...
Replies
5
Views
1K
Doing a lot of EICRs at the moment and have came across what I'm sure is a common enough problem. In an off grid rural cottage I have a TT system...
Replies
20
Views
3K
TNC-S main supply with 16mm swa supplying garage consumer unit from main consumer unit in house, then 4mm swa supplying pond equipment through...
Replies
36
Views
3K
Hi guys I was recently ask by a customer if/how his house could be supplied by his electric car. He wants to charge the car at night on low rate...
Replies
4
Views
1K
As the title says, I am looking for a recommendation for an enclosure and gland arrangement to electrically isolate or divorce the earth/armouring...
Replies
25
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock