R Rosstac Feb 20, 2024 #1 What tests and certification do you do for motors supplied via a motor control panel, DoL, soft starts, VSD, star delta, etc?
What tests and certification do you do for motors supplied via a motor control panel, DoL, soft starts, VSD, star delta, etc?
D davesparks Feb 20, 2024 #2 For the supply to the panel or starter a standard BS7671 set of tests. For the outgoing circuits test according to the requirements of the designer.
For the supply to the panel or starter a standard BS7671 set of tests. For the outgoing circuits test according to the requirements of the designer.
ipf ~ Mentor Arms Mar 5, 2024 #3 Fortnight and no thank you. One post wonder who couldn't care a tinker's, maybe?
A alexcarnes Apr 12, 2024 #4 davesparks said: For the supply to the panel or starter a standard BS7671 set of tests. For the outgoing circuits test according to the requirements of the designer. Click to expand... I've often wondered about this too. How useful are earth fault loop impedance tests/measurements when the motor has a VSD? I presume the fault current is severely limited by the inverter, so the phase fuses in the panel are just to protect the panel itself?
davesparks said: For the supply to the panel or starter a standard BS7671 set of tests. For the outgoing circuits test according to the requirements of the designer. Click to expand... I've often wondered about this too. How useful are earth fault loop impedance tests/measurements when the motor has a VSD? I presume the fault current is severely limited by the inverter, so the phase fuses in the panel are just to protect the panel itself?