I posted a question about motor overloads yesterday and this is a follow up. my client (the pool builder) has asked me to provide the FLC and starting current for the Architect to work out the required house supply. Why would the architect need to know the starting current?
 
I posted a question about motor overloads yesterday and this is a follow up. my client (the pool builder) has asked me to provide the FLC and starting current for the Architect to work out the required house supply. Why would the architect need to know the starting current?

I'm assuming that this install is part of a much bigger project install and as such needs to be assessed. It'll be the Architects electrical consultant that needs the information in order to determine the overall installations ''Max Demand'' and this will be put forward to the DNO in the form of a KVA value.
 
yes I understand that, and I can see why he would need FLC but why starting current?

The DNO need to know this to assess where they bring the new supply in from. Big starting currents can cause problems for other people fed from the same supply/cable, flickering lights etc.

They assess this then decide where along the cable to tap off from.
 
I presume then, that this would be a generic form that the DNO has provided to the architect, and they actually won't need the information for a pump this small but as its on the form the architect feels he needs to fill it in.
 
I presume then, that this would be a generic form that the DNO has provided to the architect, and they actually won't need the information for a pump this small but as its on the form the architect feels he needs to fill it in.

Seems like it as it does ask on the form. Just say 1 amp lol...
 
I posted a question about motor overloads yesterday and this is a follow up. my client (the pool builder) has asked me to provide the FLC and starting current for the Architect to work out the required house supply. Why would the architect need to know the starting current?

IMO he would NOT require to know the starting current of this motor as it would be for only a couple of seconds and this would not affect cable ratings.
Oops see engineer 54 has mentioned something similar.
 
I think he's just dotting all the i's and crossing the T's ..... 7.5kw motors DOL and above are quite capable of taking out a 100A service fuse on start-up and they will be aware of this fact that some motors pose a issue although not a concern for you here..... if the installation is going to be heavy loaded then a smaller KW motor may also cause issues especially if the service cutout fuse is lower rated i.e. 60amp or 80amp.

As suggested he will be filling out a DNO supply request or upgrade and it will ask to confirm any motors etc and size that may be in use.... excluding the obvious tiny domestic vac, fans etc.

Also they need to know the effects of any volts drop created on the supply as it may cause nuisance transients on neighbours supply like lights dimming for a second etc etc they are very strict on anything that will cause a high inrush of current as it effect other customers.
 
7.5KW DOL with the correct protection will not take out a BS88 service fuse. I will say that categorically!

Where there could be a problem is in disturbance on the local power network. If the area supply is weak then a DOL motor starting will cause problems with voltage dips and transient harmonics.

Do you have information regarding the area supply? It would help if you have.

OK you’ve got me interested with this one. Get the information and I’m sure E54, DW and I will sort it.
 
Ill refine my understanding of the 7.5kw then its as i was taught that 7.5kw and above should be 'soft' started if the supply is a standard 100amp service.... but was told this is effectively because both issues of transients as mentioned and the possibilty of service fuse rupture.... however this possibility maybe highly unlikely but still may exist so ill dig deeper on that issue myself and see if i can understand better why i was taught that......
 