Hi Guys,

a woman phoned me about moving her consumer unit up the wall ( about 500mm),

Its a 5 way board with mcbs and cables come from below up the cavity wall,

the meter is back to back to the board

I was just wondering what the best way to approach this would be or any advice would be great

for example,it's wired in the old colour code so would it be ok to join cables that wont reach new position?

thanks
 
I'm sure everybody will have a different approach but I would use wago boxes / maintenance free junction boxes to extend the cables and hide the boxes somewhere safe. Not keen using crimps on twin and earth.
 
I'm sure everybody will have a different approach but I would use wago boxes / maintenance free junction boxes to extend the cables and hide the boxes somewhere safe. Not keen using crimps on twin and earth.


would I have to upgrade the board to rcd protected as there are no rcds present?
 
Yes, its a major alteration requiring an EIC so you must insure the part you work on meets 17th edition as well as bonding, tails etc and part p notification
 
another way is crimp adding heat shrink sleeving but leave all terminations accessible in box trunking make sure certs describe what has been done
 