There are 4small juice dispensers (incorporates a chiller in each), a small salad (coldmeats) chiller and a fridge on a circuit protected by a 20Amp MCB. NONE ofthese items are on plugs and are attached to the circuit via 20Amp 4pole rotary isolators.
All the items when they arrived new were fitted with European plugs (2pin) rated at16Amps each.
The flex for each item is between 0.8mm and 1.5mm and a max of 1.5m long.
My questionis as the devices have motors / compressors for the chillers; they are not afixed load (like a luminaire) and may suffer ‘Overcurrent’ thus the cables could fail (melt) before the MCB trips. But the chillers only pull 500w on a .8mm cables. So is it acceptable to run the small juicers and other equipment off the20Amp MCB?
My point of reference is 433.3.1 (ii) ……….. is not likely to carry overcurrent…. So a 2.2 Amp appliance (max load from Manufactures rating plate) burning out a 0.8mm cable.
This also happens with the split Air Con systems 20Amp MCB, 20Amp Isolator with a 1mm manufactures cable to the unit (max load from rating plate 5.6Amp) 2-3 A/C per MCB. These are being picked up by a group of inspectors as a danger as the MCB is 20A. But the load is sub 6Amp
Is this adanger as I think not….. but I’m ready to be educated (chapter and verse would be appreciated as a reference please) !
All the items when they arrived new were fitted with European plugs (2pin) rated at16Amps each.
The flex for each item is between 0.8mm and 1.5mm and a max of 1.5m long.
My questionis as the devices have motors / compressors for the chillers; they are not afixed load (like a luminaire) and may suffer ‘Overcurrent’ thus the cables could fail (melt) before the MCB trips. But the chillers only pull 500w on a .8mm cables. So is it acceptable to run the small juicers and other equipment off the20Amp MCB?
My point of reference is 433.3.1 (ii) ……….. is not likely to carry overcurrent…. So a 2.2 Amp appliance (max load from Manufactures rating plate) burning out a 0.8mm cable.
This also happens with the split Air Con systems 20Amp MCB, 20Amp Isolator with a 1mm manufactures cable to the unit (max load from rating plate 5.6Amp) 2-3 A/C per MCB. These are being picked up by a group of inspectors as a danger as the MCB is 20A. But the load is sub 6Amp
Is this adanger as I think not….. but I’m ready to be educated (chapter and verse would be appreciated as a reference please) !