First off, hands up I am a five week wonder, currently working with a 'proper' spark and getting lots of valualble experience, anyway, my Dad phoned this morning saying that the downstairs ring main had tripped and would not reset, unfortunately I don't live very nearby so he will have to call in a spark, but I did go through some steps.
Firstly its the MCB thats tripping not the RCD, this presumably means a Live/ Earth fault of more than 32 amps on that circuit.
Next step was to get him to unplug everthing he could think of on that ring, did that and the MCB will still not reset.
Next I checked that he hadn't bought any new appliances or had any work done lately, all negative.

I was wondering what your next steps would be if you were the spark that was called out, presumably you would check PFC and Ze and check the CU to make sure nothing was hanging in the breeze that shouldn't be, next I guess would be a IR test (if everything is unplugged), after that I guess it would be front covers off the socket outlets to check them. Do MCB's often fail, could this be a cause?

Anyway, any replies gratefully received.

Down2earth.
 
After the obvious like a visual check of the CU and the sockets and making sure everything's unplugged I would test the MCB without the circuit connected then start splitting up the offending circuit to localise the fault with a tester.

MCB's do go faulty if they're cheapies, it's fairly unusual if it's a good brand make though.
 
If you have an RCD protected circuit where the MCB is tripping then this is a fault from Line to Neutral, there is no fault to earth.
If the MCB is tripping instantly, i.e. will not reset after time this is likely a direct short. With the circuit disconnected a L-N insulation resistance test would confirm this but if it is a direct short then continuity could be used. Assuming no apliances, plugged on on FCUs are connected then split the ring and start narrowing down the fault location. Usually (if no one has been hammering nails in) the fault will be at a socket outlet.

(Marvo, you beat me to it again!)
 
Last edited:
I would change the MCB as a matter of course. It’s either faulty, or it’s been closed on to a fault quite a few times now. Operating on a fault will knock the stuffing out of it.
 
Not really a helpfull answer but I nearly spat my tea over my laptop when I 1st read the thread title......Just my warped mind sorry.
 
First off, hands up I am a five week wonder, currently working with a 'proper' spark and getting lots of valualble experience, anyway, my Dad phoned this morning saying that the downstairs ring main had tripped and would not reset, unfortunately I don't live very nearby so he will have to call in a spark, but I did go through some steps.
Firstly its the MCB thats tripping not the RCD, this presumably means a Live/ Earth fault of more than 32 amps on that circuit.

Are you sure?

Next step was to get him to unplug everthing he could think of on that ring, did that and the MCB will still not reset.
Next I checked that he hadn't bought any new appliances or had any work done lately, all negative.

I was wondering what your next steps would be if you were the spark that was called out, presumably you would check PFC and Ze and check the CU to make sure nothing was hanging in the breeze that shouldn't be, next I guess would be a IR test (if everything is unplugged), after that I guess it would be front covers off the socket outlets to check them. Do MCB's often fail, could this be a cause?

Anyway, any replies gratefully received.

Down2earth.

If the RCD is not tripping then i doubt is an earth fault more like a short L-N, you would need a large PEFC to cause a MCB to go before the RCD.

Regards Chris
 
For those of you who won't be able to sleep tonight without knowing what the problem was, it turns out the conservatory light was full of water as the wind had been blowing the rain up the roof, I assume the light is on a switched fuse spur off the downstairs ring.

Thankyou all for your replies, and TGIF.

Down2earth.
 
For those of you who won't be able to sleep tonight without knowing what the problem was, it turns out the conservatory light was full of water as the wind had been blowing the rain up the roof, I assume the light is on a switched fuse spur off the downstairs ring.

Thankyou all for your replies, and TGIF.

Down2earth.

Its always a good idea to mount the lights on the inside of the conservatory roof - :D
 
For those of you who won't be able to sleep tonight without knowing what the problem was, it turns out the conservatory light was full of water as the wind had been blowing the rain up the roof, I assume the light is on a switched fuse spur off the downstairs ring.

Thankyou all for your replies, and TGIF.

Down2earth.
knowing conservatory fitters, it's just as likely to come direct off the cooker isolator in telephone wire.
 
Not really a helpfull answer but I nearly spat my tea over my laptop when I 1st read the thread title......Just my warped mind sorry.

could have been worse,his dad might of had a problem with his male chicken..:shades_smile:
 