kkelsey342

I have existing 230V 1P circuit (L1, L2 & Neutral) out at my deep well head. There is no practical to install/run additional circuit(s) to this location without incurring allot of expense... I need to obtain (or create) a "seperate" 120V 1P curcuit (to use in creating a set of low voltage controls) off of the existing 230V circuit..

Can I simply tie off of L1 and the Neutral to creat the seperate 120V 1P circuit I need???

Thanks for any advice!
 
Why not put a 230v primary 120v secondary control transformer in the box with the rest of the control gear?
 
I have existing 230V 1P circuit (L1, L2 & Neutral) out at my deep well head. There is no practical to install/run additional circuit(s) to this location without incurring allot of expense... I need to obtain (or create) a "seperate" 120V 1P curcuit (to use in creating a set of low voltage controls) off of the existing 230V circuit..

Can I simply tie off of L1 and the Neutral to creat the seperate 120V 1P circuit I need???

Thanks for any advice!
Do you still use your well. If not you won’t be able to use one leg of the 240vac leg because you don’t have a neutral.
 
Do you still use your well. If not you won’t be able to use one leg of the 240vac leg because you don’t have a neutral.
You say you have a neutral but all you have is 2 hots and 1 ground. I’ve wired many wells and I have yet to run across one that requires a neutral.
 
Why not put a 230v primary 120v secondary control transformer in the box with the rest of the control gear?
Thanks James... I want to say "duh..." because I was actually looking at the very transformer you mention... I guess I was just focused on wanting to use one leg and the neutral...
 
You say you have a neutral but all you have is 2 hots and 1 ground. I’ve wired many wells and I have yet to run across one that requires a neutral.
Thanks... Here where I am (Central Texas)... current code actually requires a 4-wire circuit "down the hole". Thus, I have 2 Hots, a Neutral and a Ground...
 