You have jumped in the definitions that Sisyphus posted from neutral conductor to neutral point.
I think he was just trying to help. I welcome any knowledge or new way of looking at something. He posted neutral point because by the looks of it in order for a conductor to be called a neutral under the NEC it must have a symmetrical phase angle relative to two or more live conductors. In order for uch to take place, it must originate from a central neutral point at the source.
In either case of BS7671 or 14 NEC the neutral conductor is one that has a (near) zero potential and is intended to carry current, as Lucien said in post 5.
From the definition in BS7671, the secondary of a two wire earthed AC supply should not be called a neutral conductor. A 2 wire DC yes, but not AC.
In terms of your example if it is a TNCS supply then the neutral from the transformer would also be the earth conductor so the conductor would be a protective earth neutral conductor or PEN conductor.
Correct, but in neither (TN-S or PME) case should it be called a neutral when referring to the regs.