Whilst i can only recommend i just think a new consumer unit would enhance the safety of the installation. It would be more accessible, provide extra ways for circuits that are doubled up. There seems to be quite a few sockets that are spured of an already unfused spur from the ring. I was going to suggest splitting the ring into two radials, but again there is no room in the current unit. If im classing the boiler supply as a C2 and the customer wants a report that is satisfactory i really cant see how i am going to go about replacing the MCB for one of a lower rating
 
IMG_5023.JPG
IMG_5024.JPG
IMG_5026.JPG
IMG_5028.JPG
 
What's the story with the shower?
 
Nice!
 
Don't get yourself into the customer wants a satisfactory report game. Take the advice I was given when it went pear shaped for me. Report and if they want the work doing, quote for it as a separate work item.

If you can't squeeze a new MCB in that board, then could you not take an SFCU from the ring close to the boiler and then disconnect that circuit at the CU?
 
6mm2 T&E feed that has been extended with through crimps inside the shower unit using 2.5mm

Deffo C2 and unsatisfactory.

Submit invoice and report.....

A satisfactory report will need more money spent...... So get paid for the report
 
  • Like
Reactions: Des 56
Don't get yourself into the customer wants a satisfactory report game. Take the advice I was given when it went pear shaped for me. Report and if they want the work doing, quote for it as a separate work item.

If you can't squeeze a new MCB in that board, then could you not take an SFCU from the ring close to the boiler and then disconnect that circuit at the CU?
Not without alot of disruption to decoration, that consumer unit is a nightmare to work in. Its just about accessible for the user if anything trips.
 
Did they build the stairs around the DB?
That is a tight space and with that stupid shaped shelf that doesn't help changing the board will be as much work if not more!
Question 2 Is the husband still around or has she buried him?
 
  • Funny
Reactions: Des 56 and DPG
Did they build the stairs around the DB?
That is a tight space and with that stupid shaped shelf that doesn't help changing the board will be as much work if not more!
Question 2 Is the husband still around or has she buried him?
Yeah he's still around, he was giving it the " i dont know why she wants this work done its been fine for years " line, when i was there. Thinking of moving the DB directly under that shelf if possible. I certainly wouldnt want to keep it in there
 
time to get the hammer out.
 
The customer is aware that if they require a satisfactory report then they are going to have to spend more money to have the remedial work done. Once i have copied the report from draft form i am going to have a sit down with them to discuss there options

I think I'd get my bill in before talking though any of it with them to be honest
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

leep82

Arms
~
Joined
Location
Stoke on Trent
Business Name
L.M.P Electrical

Thread Information

Title
Neutral-Earth voltage
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
36

Advert

Thread statistics

Created
leep82,
Last reply from
davesparks,
Replies
36
Views
9,163

Advert