Called to a property yesterday after the customer had been advised to call an electrician by an engineer who had done some work on there cooker. I arrived and was directed towards a socket in the kitchen. The lady couldnt really explain what the engineer had told her.

I plugged my multifunction tester in and immmediately realised there was a problem. The display wasnt showing a voltage between live and earth but was showing voltage between live-neutral and neutral-earth. I removed the socket front and saw that the live and neutral conductors had been connected into the wrong terminals. Once i had sorted this out i plugged my tester in again to try and do a Zs test, but i was unable to as there was still voltage showing between neutral and earth. I tried another socket in the kitchen on the same circuit and was able to perform the test, getting a reading of 500ohms. The system is a TT although a quick look at the mains suggests there might be PME available.

I went around various sockets on the circuit and was left a little bit baffled as some would let me perform a Zs test and others wouldnt as it was indicating a voltage between neutral and earth. When i initially removed the socket with reversed polarity i used my tester across neutral and earth and was getting a voltage of around 30v. I have advised the customer to have a EICR, which she is going ahead with. I wasnt able to spend any great deal of time there last night so sorry for any lack of other information. As already said i will be returning to carry out an EICR so will hopefully get to the bottom of the issue then, but in the meantime any suggestions, advice greatly welcomed.
 
Not uncommon on TT systems.
 
What voltages (L-E, L-N, N-E) were at the main incomer?
 
It isn't uncommon to detect small voltages on TT systems but yours seems problematic.
 
Sounds like no or poor earth to me.

Did you check the R1 + R2 on the cooker circuit?
 
Hi guys finally got back to this property at the weekend to carry out the EICR. First thing i checked was the main earthing conductor, which had corroded within its enclosure and was providing no means if earthing. I put a new clamp on and took a Ze reading ( 41 ohms ). As i started to remove accesories for inspection it became clear that the installation was in quite a poor state.

A couple of things i picked up in was that a supply to the shed was wired in 1.5mm swa, and protected by a 32a mcb. I disconnnected this and informed the customer. Unfortunately there is no room inside the DB to install a smaller rating MCB. I have left this disconnected for the time being. I also noticed a 2.5mm T&E protected by a 32a MCB i again disconnected this as i couldnt identify what it was supplying. It has since become apparant that this was the supply to the boiler. What code would this warrant as far as my observations are concerned?

Although the installation is a mess there seems to be little reason to report it as unsatisfactory. Understanding that an EICR is not a means of quoting for remedial work i really feel that the installation would benefit from a new consumer unit given some of the C3's that i have raised. The existing consumer unit is not very accesible at all for inspection and maintenance, and poorly fixed, circuits have been doubled up into the same OCPD. And although PME is available the system as mentioned is still on a TT. Should i recommend a new consumer unit based on the report?
 
Personally I'd C2 the oversized breaker for the boiler, advise replacement with a 16A on the cert.

When you say some circuits are doubled up, what? And how many? And what other reasons do you have for suggesting a replacement CU?

When you say PME is available, is that at the head or have you just confirmed with the DNO that PME is an option?
 
A couple of things i picked up in was that a supply to the shed was wired in 1.5mm swa, and protected by a 32a mcb. I disconnnected this and informed the customer. Unfortunately there is no room inside the DB to install a smaller rating MCB. ?

So are you suggesting that the SWA was connected to a MCB with another circuit? Possibly a RFC? If so, this is no different to a spur at the CU!

I don't think you can justify disconnecting circuits from 32A breakers - they are C2 at worse, certainly not C1's
 
Last edited by a moderator:
  • Agree
Reactions: SparkyChick
What type of board is this, are the mcb's still available and can't you just swap out the two 32 amp breakers for 16 amp? A board change seems overkill to me.
 
  • Agree
Reactions: SparkyChick
So are you suggesting that the SWA was connected to a MCB with another circuit? Possibly a RFC? If so, this is no different to a spur at the CU!

I don't think you can justify disconnecting circuits from 32A breakers - they are C2 at worse, certainly not C1's
Yeah the swa was in with the ring final circuit, and it wasnt terminated correctly. No gland just stripped and taken in through a knockout in the board. There is absolutely no room whatsoever to make it off into an enclosure or even into the board itself. I will try to upload a pic. The DB is in a really poor location
 
IMG_5034.JPG
 
Looks room to accommodate a adaptable box in there, then run 2.5 to the MCB

The point of an EICR is to report..... sure a shiny new CU would make sense, but for many customers they have higher priorities.

What is the purpose of the report?
 
Looks room to accommodate a adaptable box in there, then run 2.5 to the MCB

The point of an EICR is to report..... sure a shiny new CU would make sense, but for many customers they have higher priorities.

What is the purpose of the report?
There really isnt room. I cant even get my head in level with the board because of the slope of the staircase behind me. The report is at the request of the homeowner, basically her husband as done bits of DIY over the years and shes never been 100% happy with it.
 
  • Like
Reactions: DPG
^^ do report, submit with invoice and walk away - awaiting payment - do nothing until payment is received.
 
Whilst i can only recommend i just think a new consumer unit would enhance the safety of the installation. It would be more accessible, provide extra ways for circuits that are doubled up. There seems to be quite a few sockets that are spured of an already unfused spur from the ring. I was going to suggest splitting the ring into two radials, but again there is no room in the current unit. If im classing the boiler supply as a C2 and the customer wants a report that is satisfactory i really cant see how i am going to go about replacing the MCB for one of a lower rating
 
What's the story with the shower?
 
Nice!
 
Don't get yourself into the customer wants a satisfactory report game. Take the advice I was given when it went pear shaped for me. Report and if they want the work doing, quote for it as a separate work item.

If you can't squeeze a new MCB in that board, then could you not take an SFCU from the ring close to the boiler and then disconnect that circuit at the CU?
 
6mm2 T&E feed that has been extended with through crimps inside the shower unit using 2.5mm

Deffo C2 and unsatisfactory.

Submit invoice and report.....

A satisfactory report will need more money spent...... So get paid for the report
 
  • Like
Reactions: Des 56
Don't get yourself into the customer wants a satisfactory report game. Take the advice I was given when it went pear shaped for me. Report and if they want the work doing, quote for it as a separate work item.

If you can't squeeze a new MCB in that board, then could you not take an SFCU from the ring close to the boiler and then disconnect that circuit at the CU?
Not without alot of disruption to decoration, that consumer unit is a nightmare to work in. Its just about accessible for the user if anything trips.
 
Did they build the stairs around the DB?
That is a tight space and with that stupid shaped shelf that doesn't help changing the board will be as much work if not more!
Question 2 Is the husband still around or has she buried him?
 
  • Funny
Reactions: Des 56 and DPG
Did they build the stairs around the DB?
That is a tight space and with that stupid shaped shelf that doesn't help changing the board will be as much work if not more!
Question 2 Is the husband still around or has she buried him?
Yeah he's still around, he was giving it the " i dont know why she wants this work done its been fine for years " line, when i was there. Thinking of moving the DB directly under that shelf if possible. I certainly wouldnt want to keep it in there
 
time to get the hammer out.
 
The customer is aware that if they require a satisfactory report then they are going to have to spend more money to have the remedial work done. Once i have copied the report from draft form i am going to have a sit down with them to discuss there options

I think I'd get my bill in before talking though any of it with them to be honest
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

leep82

Arms
~
Joined
Location
Stoke on Trent
Business Name
L.M.P Electrical

Thread Information

Title
Neutral-Earth voltage
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
36

Advert

Thread statistics

Created
leep82,
Last reply from
davesparks,
Replies
36
Views
9,160

Advert