Wind up ?
Don't think so but the OP really should be cornering the spark that changed the CU with all the info on this thread. Definitely for the EIC and wanting to know when the certificate of compliance will be sent through and who from. . . . . . .
Why do I have that nagging feeling that there's no intention of this being notified?
I'm not in disagreement with you, though my first thought on things like kettles welded is 'how well were they wired in the first place?'

Well back to the issue of the Mcb Tripping and not the Rcd . if you think logically about this if the Mcb trips out you have a live to neutral fault .If the Rcd trips out you have a live to earth fault . Did your electrician test all circuits when he installed new board
Well back to the issue of the Mcb Tripping and not the Rcd . if you think logically about this if the Mcb trips out you have a live to neutral fault .If the Rcd trips out you have a live to earth fault . Did your electrician test all circuits when he installed new board
Or Live to CPC Earthed part.if you think logically about this if the Mcb trips out you have a live to neutral fault
Or Neutral to any Earth.If the Rcd trips out you have a live to earth fault .
tbh if I had not of started this thread I would not of known that I need the EIC, and looking online, there def was not one with the paperwork he handed me. So I will be chasing this up. All i was aware is that it has to be done by a qualiifed electrican.
well, having seen plugs welded into sockets on just 2kW kettles, either their calculations are wrong, or sockets compliant with BS1362 just ain't.
Accepted.Being pedantic here but
Live = line and neutral
Trust me this house is an electrical nightmare, what scares me the most the previous owner was an electrican. Dont worry hes not done any work to my house since i bought it lol. He has normal grey PVC cabling powering outside sockets, the garage etc etc. Im slowly getting stuff corrected and done right.