So what has he given you then??

Spoke to him today its all sorted the reason he did not issue the EIC is because, he will be coming back new year to finish the rewiring off in garage once i done the cable routing etc, all monkey work.

i would be concerned as to why he bypassed the garage rcd as it was tripping,

im having the garage rewired in new year, as tbh its sub standard. there so many bodges to it, it needs sorting.


There's nothing inherently wrong with using T&E outside as long as it is installed properly, on a wall, in conduit for example.

well thats the issue lol as its just exposed to sunlight, and the pvc is very brittle.
 
Spoke to him today its all sorted the reason he did not issue the EIC is because, he will be coming back new year to finish the rewiring off in garage once i done the cable routing etc, all monkey work.



im having the garage rewired in new year, as tbh its sub standard. there so many bodges to it, it needs sorting.




well thats the issue lol as its just exposed to sunlight, and the pvc is very brittle.

So we are closing in on the truth then!

YOU are doing some of the work. Get the sparky back in and pay him to do the lot.
 
So we are closing in on the truth then!

YOU are doing some of the work. Get the sparky back in and pay him to do the lot.

Im not doing anything wrong with drilling the holes, ripping up floor boards and plaster board, so all he has to do is wire it up and connect it all then check it.
 
its difficult to explain but the garage is set back from the house, I have and extension on the back of the house which connects to the garage. they way the previous owner has done the electrics to the house is run a grey pvc cable, no protection what so ever fromt he front of my house to the rear. Yes i could get the sparky to put new cable in to garage, but i dont want trunking running down side of the house. so im ripping up floor boards front to back to run the cables through into the extension then through to the garage.

Yes i would love someone to do this for me but im trying to save some money where i can, complying within the new regulations. also at same time im also placing cable ready to fit some mains smoke alarms. then all my elctrican will have to do is check the wiring complies and wire it all up. Im not doing any of the actual wiring myself just the work i can. Im not a DIY bodge it monster that i think your labelling me as. I believe in a firm rule 'Do the job once and do it right'
 
its difficult to explain but the garage is set back from the house, I have and extension on the back of the house which connects to the garage. they way the previous owner has done the electrics to the house is run a grey pvc cable, no protection what so ever fromt he front of my house to the rear. Yes i could get the sparky to put new cable in to garage, but i dont want trunking running down side of the house. so im ripping up floor boards front to back to run the cables through into the extension then through to the garage.

Yes i would love someone to do this for me but im trying to save some money where i can, complying within the new regulations. also at same time im also placing cable ready to fit some mains smoke alarms. then all my elctrican will have to do is check the wiring complies and wire it all up. Im not doing any of the actual wiring myself just the work i can. Im not a DIY bodge it monster that i think your labelling me as. I believe in a firm rule 'Do the job once and do it right'

I'm not labelling you as anything. You are the latest of a growing line of posters posting a very small part of a issue then expanding beyond belief.

I refer you back to your original post:

http://www.electriciansforums.net/e...8-new-cu-fitted-few-teething-issues-sort.html
 
@Murdoch. I think you are coming across a bit harsh here. The OP said much earlier (start of the 2nd page I think) he was doing some of the work to save cost. If his electrician is happy with this and happy that he will have visibility of all the work so can sign it off then what is the problem?

I don't see anything wrong with this......
 
OP did the sparks who did the DB change for you not explain the problems that may arise from fitting a 17th edition board?
 
OP did the sparks who did the DB change for you not explain the problems that may arise from fitting a 17th edition board?

yeah he did. I do realise that going from the old style wired fuses to a new CU will create issues. but the house is a 1965 build and there appears to be no modernisation since the original install. so im trying to bring the hose up to near near damm it current building regs. the old fuses are rubbish.
 
yeah he did. I do realise that going from the old style wired fuses to a new CU will create issues. but the house is a 1965 build and there appears to be no modernisation since the original install. so im trying to bring the hose up to near near damm it current building regs. the old fuses are rubbish.

In that case you have the wrong trade i. Working for you.

Seriously though, you are doing the right thing but why not get all the problems sorted at the same time as the DB change?
 
Seriously though, you are doing the right thing but why not get all the problems sorted at the same time as the DB change?

As said earlier in the thread down to money, espically this close to christmas. I know it will prob save me money in the long run, but im also trying to coinside with decorating etc, and routing some of the ccbales so all he has to do is wire it up.
 
Fair enough. But why has he the garage been left on only a MCB? If as you say the wiring is in a mess? Surely this makes a mockery of having the mew DB installed
 
just an updated have fitted a new imm element and the MCB is still tripping. The MCB is a 6amp. I would of said 6amp isnt correct should be 16amp/20amp type B?
 
Last edited by a moderator:
What is the rating of the immersion element (watts)? This should help you answer that. Daz
 
just an updated have fitted a new imm element and the MCB is still tripping. The MCB is a 6amp. I would of said 6amp isnt correct should be 16amp/20amp type B?

Yes ..... the 6 amp MCB is very probably too small, but don't just go stuffing a bigger one in without first knowing how much current you immersion heater is drawing.

If you know its rating (how many watts it is) you can work out how many amps it draws from the formula: I = P/u which in layman's terms is Amps = Watts/Volts

SO *if* your immersion heater is 3kW it is 3,000/230 = 13.04 Amps. In this case, you need to be looking to fit a 16amp MCB but it's all depending on how many watts your immersion is rated at so you need to check that first.

Always use the figure 230 for your volts BTW.
 