My correction was commenting on where you said that as long as everything was protected by a 30mA RCD then there was no requirement to fit a 100mA TD. This implies that there then WOULD be a requirement to fit a 100mA TD should there not be 30mA protection elsewhere, which is wrong, as there is no requirement to fit 30mA RCD protection in the first place. If you can meet disconnection times using 300mA RCDs then there's nothing to stop you using them, also, achieve stable TN values on a TT and there's no requirement to use an RCD at all.

My ONLY point is that when utilising ADS as a protective measure it is a common misconseption that we are bound by regulation to use 30mA RCDs on TT systems.


Maybe, .....But i think you'd need to be an absolute idiot, not to incorporate RCD/RCBO 30mA protection on a domestic TT installation no-matter what it says in the BGB and it's OSG's!!

Likewise, i can't see any problem replacing the CU's main switch with an S type RCD either. It's a rated DP switch at the end of the day, with a time delayed earth leakage facility. The time delayed RCD feature would comply with 1 sec disconnection times (or pretty dammed close) in the event of an actual fault, in the event of the downstream 30mA devise failing for whatever reason to clear the fault....
 
Maybe, .....But i think you'd need to be an absolute idiot, not to incorporate RCD/RCBO 30mA protection on a domestic TT installation no-matter what it says in the BGB and it's OSG's!!

Agreed! But like I said, I was just dispelling a myth and a common misconception, nothing more.

Likewise, i can't see any problem replacing the CU's main switch with an S type RCD either. It's a rated DP switch at the end of the day, with a time delayed earth leakage facility. The time delayed RCD feature would comply with 1 sec disconnection times (or pretty dammed close) in the event of an actual fault, in the event of the downstream 30mA devise failing for whatever reason to clear the fault....

If it is replacing a main switch then it is not protecting a distribution circuit, therefore it is bound by the 0.2s disconnection time which it won't meet. A type-s must be fitted ahead of the DB. This will also protect against every type of earth fault that could possibly arise within the DB also (however unlikely).
 
Can't quite understand the arguement about not providing an 30ma rcd for final circuits, how do you achieve discrimination with just a 100ma rcd, or am i misunderstanding things here?

I'm not quite sure I understand your question?

If your question is regarding discrimination of RCDs, there's no such thing unless they incorporate a time delay feature.
 
On the basis that you don't need RCD protection for the tails, just stick in an insulated CU and a dual RCD board or one full of RCBO's
 
Agreed! But like I said, I was just dispelling a myth and a common misconception, nothing more.



If it is replacing a main switch then it is not protecting a distribution circuit, therefore it is bound by the 0.2s disconnection time which it won't meet. A type-s must be fitted ahead of the DB. This will also protect against every type of earth fault that could possibly arise within the DB also (however unlikely).

Yes, your right i must having been thinking of something else i was doing yesterday....

But as for the rest of the above, I honestly can't see there being any difference whatsoever in placement position, be it inside as the main switch, or outside of the CU/DB, it'll be doing exactly the same job, of looking after the installation as a whole!! I wouldn't think twice about using a S type RCD as the main switch, in fact that's exactly what i have done in my own house, all be it a 3 phase Jobey!!
 
reminds me of a chap i used to work for...
he installed a temporary rod to an install with no earth (waiting for the DNO to come out and sort it)....
i asked if he was going to put an upfront RCD to this temporary setup
`eh?` was the reply....lol..lol...
 
If its only purpose it to provide back up protection to nothing other than the final circuits for which regulation doesn't cover as it exceeds the minimum standard set down in regulation then yes, it aint gonna matter where it's put as protection against single fault conditions has been catered for by the RCDs in the DB, I suppose it's down to personal choice, so long as you're happy with the DB being unprotected which if class 2 isn't really that important anyway.

Personally, I always fit them up front in their own plastic enclosure. They double up then as an isolator too. Much more useful and I can also then fit metal DBs as I hate plastic ones :)
 
If its only purpose it to provide back up protection to nothing other than the final circuits for which regulation doesn't cover as it exceeds the minimum standard set down in regulation then yes, it aint gonna matter where it's put as protection against single fault conditions has been catered for by the RCDs in the DB, I suppose it's down to personal choice, so long as you're happy with the DB being unprotected which if class 2 isn't really that important anyway.

Personally, I always fit them up front in their own plastic enclosure. They double up then as an isolator too. Much more useful and I can also then fit metal DBs as I hate plastic ones :)

Yep i'll go along with that too, but i thought this was about replacing the main switch for a S type RCD.

To be honest i don't pay too much attention to this crap about TT installs shouldn't have metal CU's in case the tails short out on the metal entry apertures. Nothing that suitable PVC bushing or glanding can't handle, considering that typical tails are insulated and sheathed anyway!!
 