Chint, hmmmm not sure! but do work.
CGD I think are OK, I have used them no real problems but not used many.
CGD I think are OK, I have used them no real problems but not used many.
dont know but chint have a kind of `chinese` ring about em...Chint, hmmmm not sure! but do work.
CGD I think are OK, I have used them no real problems but not used many.
LOL, too True what a silly thread haha, talk about over complicating a simple Jobwhat a ramble all this is...
get yourself a split load board with 2X 30mA RCDs...
My correction was commenting on where you said that as long as everything was protected by a 30mA RCD then there was no requirement to fit a 100mA TD. This implies that there then WOULD be a requirement to fit a 100mA TD should there not be 30mA protection elsewhere, which is wrong, as there is no requirement to fit 30mA RCD protection in the first place. If you can meet disconnection times using 300mA RCDs then there's nothing to stop you using them, also, achieve stable TN values on a TT and there's no requirement to use an RCD at all.
My ONLY point is that when utilising ADS as a protective measure it is a common misconseption that we are bound by regulation to use 30mA RCDs on TT systems.
Maybe, .....But i think you'd need to be an absolute idiot, not to incorporate RCD/RCBO 30mA protection on a domestic TT installation no-matter what it says in the BGB and it's OSG's!!
Likewise, i can't see any problem replacing the CU's main switch with an S type RCD either. It's a rated DP switch at the end of the day, with a time delayed earth leakage facility. The time delayed RCD feature would comply with 1 sec disconnection times (or pretty dammed close) in the event of an actual fault, in the event of the downstream 30mA devise failing for whatever reason to clear the fault....
Can't quite understand the arguement about not providing an 30ma rcd for final circuits, how do you achieve discrimination with just a 100ma rcd, or am i misunderstanding things here?
Agreed! But like I said, I was just dispelling a myth and a common misconception, nothing more.
If it is replacing a main switch then it is not protecting a distribution circuit, therefore it is bound by the 0.2s disconnection time which it won't meet. A type-s must be fitted ahead of the DB. This will also protect against every type of earth fault that could possibly arise within the DB also (however unlikely).

If its only purpose it to provide back up protection to nothing other than the final circuits for which regulation doesn't cover as it exceeds the minimum standard set down in regulation then yes, it aint gonna matter where it's put as protection against single fault conditions has been catered for by the RCDs in the DB, I suppose it's down to personal choice, so long as you're happy with the DB being unprotected which if class 2 isn't really that important anyway.
Personally, I always fit them up front in their own plastic enclosure. They double up then as an isolator too. Much more useful and I can also then fit metal DBs as I hate plastic ones![]()
but i thought this was about replacing the main switch for a S type RCD.