Why would it be a 100A switch? You can get 32A switchfuses. Socomec make them among others.


The clue is in your post........what size of fuses in the cut out???????????????????
 
Yes, but your only providing over current protection for the supply to the heat pump. As such, from the Henley block you take a 6mm2 for example to the switchfuse. The 32A fuses protect that cable from overload, the 100A fuses provide short circuit protection.

If you consider a busbar chamber, you wouldn't size everything fed from it to the size of the incomer.
 
You only require one point of isolation. This is primarily the cutout. I agree that one switch in front of everything is best, but only if the customer will pay!

Why would it be a 100A switch? You can get 32A switchfuses. Socomec make them among others.