A friend of mine is having problems with his 11 year old mira shower (intermitant hot water).
Went to have a quick look today.
Old rewirable fuse board, no Rcd, 6 mm cable. No bonding.

He wants a new shower, my first advice was to stop using the original one.
To be fair the house could do with a rewire, at the very least a new board and bonding.

As he is a friend I was thinking of the cheapest way of sorting out his shower first.

As the shower backs on to the airing cupboard, was thinking of putting in a
garage supply unit with Rcd and 32 amp breaker in the cupboard, sorting out the bonding and fitting
an 8.5Kw shower.

Any thoughts?
 
doing it that way would negate the need for an unsightly, unreliable pull switch in the bathroom. can't see a problem with it. the 6mm would still need to be fused at the CU.
 
Thanks telectrix,
The main cu is a rewirable fuse.
I would leave the pull switch in, and garage supply unit would be between that and shower.
Also, as its in the airing cupboard, i would connect the earth bar to the supplementary bonding of the heating/water storage.
 
in that case, would it not be easier to fit the sub-main adjacent to the CU, then no need to disturb cabling from the pull switch?
 
Yes your correct, however access and room at the main cu would create a longer/costlier job.
Realistically the board needs updating and moving 5 feet, as he's a friend,
just wanted to do cheapest best job i could.
 
make sure thye cable in the attic is not covered in itchy-poo. that will reduce your current capacity dramatically.
 