Just turned up to a job that I haven't worked at for a few years and they have had a new supply installed as they have extended their building recently

their old supply was 200A TNS but it melted

This new one looks like a PME and 600A with a concentric supply cable

no sticker though

but its a sealed unit to main busbar/isolator so i cant really confirm anything or test at any origin of such, without some isolation which was not possible today

their bonding is now too small if it has been changed to PME, but usually the DNO are all over the bonding requirements before they put in a PME

is there any possibility its still a TNS


sorry the pic is sideways
 

Attachments

  • main.jpg
    main.jpg
    227.1 KB · Views: 76
Hi,

No doubt I will be corrected on this, but as the connection is exposed I would think TN-S. I'm ducking low awaiting the flak.


Regards.
 
Looks like the cable is 95CNE so still only 200A max supply definitely not 600A. Could be PME as no separate earth visible or it could be 4 core 95 and be SNE. Best to ask the DNO who installed it.
 