Hi all. Does anybody know roughly how much it would cost and should I go straight to local dno with the question as follows?
Require a new supply for a 2000amp machine.
The factory it would be placed in already is used at full capacity (load wise)
Not my usual area of work as im a commercial and domestic spark but ive been asked the question by somebody and would like to point them in the right direction. Thanks
 
If your DNO's are anything like our energy suppliers then a supply of that size may not even be available depending on their local network capability. Can't you just ask the DNO for a preliminary survey and an indication of costings?
 
I believe is around 800 kw.
Not my area whatsoever. I presumed I would have to direct this person to dno but thought I would raise the question with you guys as im not clued up with this type of feed.
So first step would be to tell dno the location of site and load requirements and take it from there?
 
Yes 800 kw is a large load as said above you will need to contact DNO and ask what is available ,but I would tell your customer to be ready for an extremely large cost if it can even be done.
 
I'm not sure how the UK DNO's work but I'm pretty sure you should approach them direct with the requirement at which point they'll want to do some kind of feasibility investigation or study. Chances are it may require alterations to additions or their infrastructure, I doubt they'll have that kind of capacity kicking around spare unless it's in an industrial area that was specially designated as high future expansion.
 
For that kind of supply you'll be looking at a DNO MV supply and a site based transformer. You'll not get that sort of supply in at LV. You'll be looking at some big bucks here. Less so, if the factory is already supplied at MV and the existing MV supply has enough spare capacity to add another suitably sized TX....


This company doesn't sound too clever to me, all this should of been sorted out well in advance before even purchasing such a large power consuming machine. This could take weeks or even months to sort out with the DNO, and that's ''IF'' the capacity is available, if it's not they are up s**t creek without a paddle!! lol!!
 
Contact the DNO they will send out a form to fill in or do it via email .... its highly likely in your case you will need a dedicated sub station either to front end the whole building or just the machine ... the process is usually lengthy you can't pay extra for priority so expect several weeks to have a pricing done and once accepted you can what another several weeks for work to commence. 4 to 6 months isn't uncommon and costing is subject to local network.

I had a 350Kva request priced at approx 50k and would have seen a substation built within the property and given to the DNO for adoption as their property.... this was tapping into a local 11Kv line at the top of the road.... the cost is really hard to judge too many variables.
 
Contact the DNO they will send out a form to fill in or do it via email .... its highly likely in your case you will need a dedicated sub station either to front end the whole building or just the machine ... the process is usually lengthy you can't pay extra for priority so expect several weeks to have a pricing done and once accepted you can what another several weeks for work to commence. 4 to 6 months isn't uncommon and costing is subject to local network.

I had a 350Kva request priced at approx 50k and would have seen a substation built within the property and given to the DNO for adoption as their property.... this was tapping into a local 11Kv line at the top of the road.... the cost is really hard to judge too many variables.

To upgrade the TX to cover the whole installation, will in all probability increase the KA fault rating of the existing main LV Switchboard beyond it's present designed rating. So that would incur a substantial increase to upgrade the KA/bracing rating of the Switchboard in the overall cost of the upgrade. That's assuming that the Switchboard will lend itself to increasing it's KA fault level. That's not to mention the down time of the factory while such upgrades are being made. Far better to go with an additional MV/LV TX supplying it's own LV switchboard...

So many variables here, that needs to be discussed in detail between the DNO and the customer, and as pointed out, it will be a time consuming process from initial inquiry to the day the factory can switch on this new machinery!! lol!!
 
200 or 2000A? 2000A @433V = 1500KVA. 2000A single phase, they will tell you where to go!

Where you’ve been getting your figures from I don’t know, but non of them make any sense.

Go and check you’re figures.

Just to cheer you up, a 800KVA 11KV supply to an existing transformer earlier this year £75K for the DNO supply only. Added to which new MV intake switchgear and cable were required.
 
My knowledge of DNO and larger supplies is nothing less than an 18 week wait from time of order.
That's even for relocation of the incomer on site, let alone a new supply which may have to come several hundred metres across the highway.

I suspect this thread will still be live in August whereas the Factory won't be.

This is the job for Consultants, before any contact with the DNO.

DNO will want to know exact details of what load and proposed location of incomer etc.
 