This is proving harder than finding hens teeth...
I suspect Westward10 is assuming you are a qualified electrician and thus know the Reg's, although are inexperienced is this kind of situation. I think he's being a bit "bloody minded" or "deliberately obtuse" to try to teach you be more precise and forthcoming in your questioning...
If you are not a sparky and are asking because this fault has been brought to your attention, then the current Reg's tell us there should be a CPC in your fixed wiring, but ancient Reg's did not require this for lighting circuits that were assumed to be generally out of reach and not commonly interacted with. Remember, back then copper was expensive and the country was still bankrupt (interest rates were still 17% in my youth).
It is a general principle that changes to any Regulations are not retroactive (an exception being Fire Reg's) and so if something was considered safe back then it cannot be declared unsafe now simply because technology has advanced. There are specific exceptions, where objectively danger is or will be present under fault conditions:
If any part your lighting circuit has Class I (conductive, metallic) accessories/exposed parts, then those parts must be earthed in some manner.
In your unexplained scenario, if the lighting drop feeds a metal light switch, it must be earthed. If it feeds a standard modern urea plastic switch, it need not be rectified. In the first instance the absence of earthing is C2 safety failure. In the second instance it can only be a C3 observation because the old Reg's in effect when it was installed said this was satisfactory. The same is true of the light fitting itself, whether it be Class I conductive or Class II insulated.
How was this considered safe back then? Because metal (brass) accessories were a newer posh innovation for people with money. All our light switches used to be Bakelite dolly switches on wood backboards. And there was no such thing as metal conduit or trunking, it was all hand made wooden troughs sunk and skimmed with weak cement mix. Or VIR sunk directly in shitty cinter-block and skimmed over with no capping (lead capping was too expensive until a bit later).
However (and this is where opinion comes into it, which is what Westward10 challenged you about), I would be more concerned that wiring installed when those old Reg's were in force (at least 40 years ago, I'm not looking up my old Reg's books to see when the change came in) may be in a poor state of repair in 2025 and due a rewire. It may even be installed in VIR or cotton braid. Ensure a full EICR is done (
full, i.e. Live-to-Live insulation resistance testing of all legs at 500V with all switches multiply operated) to judge the real condition of this "archaic" installation, and know that VIR can give excellent insulation resistance readings right up to the time that you have to interfere with it (e.g. by rewiring light switches) at which point any movement at all will cause the basic insulation to crack and rapidly degrade. There's nothing you can do about it: you can't tape it up, you can't cut and strip back to "good stuff" (it doesn't exist, it will powder in your fingers no matter how far up you go), the only thing you can do temporarily is feed large sleeving over it as far up as it will slide without physically moving it more to gain access.