OK, lets have a decent discussion about this as I'm sure there will be a number of opinions!

Have done an EICR on a 40 + year old flat. The lighting circuit is wired in singles and utilises the steel conduit as the CPC. Out of the 6 lights and using my R2 wander lead, only 2 have an acceptable reading - the remaining 4 have 200 ohms

The CU is a dual RCD and there are no metal fittings or switches

So do I:

A: Suggest a "no CPC" label be added and give a "satisfactory" ?

or

B: tell the owner the lighting circuit needs a rewire and give it an "unsatisfactory"?


Thanks

Tin hat on!
 
being a bit of a "old installation " geek, i'd maybe have a go at repairing the conduit cpc, if it weren't a massive job. failing that, your option A, with a recommend that the circuit/s would benefit fron either a rewire, or the addition of a cpc conductor.
 
It has a cpcs, the conduit. Lack of an earth either means the light fittings are incorrectly connected or continuity of the conduit has broken down.
 
It is never satisfactory if continuity of the conduit is breaking down. You cannot fit a notice stating no cpc because there is.
 
problem being that the conduit itself may not be earthed. it's all weel and good to use classII fittings on a light circuit with no cpc. but here you have metal conduit not earthed.
 
I suppose the conduit is the type where it is buried in the ceiling? It sounds like effectively the lighting is without a cpc and from a risk perspective I would treat it as that. The likliehood of repairing it is quite low. In which case what were your Mohm readings, presumbly good as the circuit has RCD protection. Any Class 1 fittings?
 
But as I've proved without doubt that 4 of the positions don't have earth continuity, then what would you do?
I would C2 it obviously unsatisfactory. As for correcting it, yes you could run a separate cpc if that is possible but that would be no guarantee all the conduit is effectively earthed. With such a wiring system I would probably date it 55+ years and suggest it should be rewired.
 
I suppose the conduit is the type where it is buried in the ceiling? It sounds like effectively the lighting is without a cpc and from a risk perspective I would treat it as that. The likelyhood of repairing it is quite low. In which case what were your Mohm readings, presumbly good as the circuit has RCD protection. Any Class 1 fittings?

Conduit in ceiling
RCD protection
no class 1 fittings
 
write it up as a C2 and then advise client of the options.
 
I come across this a lot testing some of the old university buildings, I class it as c2, as the conduit could become live under a fault and the protective device will not operate.
We have to rectify it either by pulling in new cpc from the DB to each point or connect a cpc from the last point where the earth reading is acceptable and then work back to the last point on the circuit, some times easier said than done!
 
IMO, singles in conduit= full conduit system, broken earth continuity in parts, c2 this is the very reason why I always pulled in a separate cpc in, on all my circuits in a full conduit system.!
 
They never used a cpc in the old days, just relied on the metal containment. Although having said that, I tested another university building built in 1991 and its all metal containment with no seperate Earth, done properly though, earth couplers, serrated washers used throughout, all good readings!
 
They never used a cpc in the old days, just relied on the metal containment. Although having said that, I tested another university building built in 1991 and its all metal containment with no seperate Earth, done properly though, earth couplers, serrated washers used throughout, all good readings!
I know, but rusty conduit concealed in walls etc after many years it fails. All council rewires I have done in the past have pulled in a cpc on existing conduit without cpc, and when you can't its all surface work.:(
 

Reply to No CPC on lighting circuit ............ in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

I've tried to research and form a plan without asking on here, but I'm just going around in circles. Just completed an EICR. The wiring ranges...
Replies
15
Views
2K
4mm T&E circuits on 32amp breaker. Parts of the circuit run through ceiling, parts through trunking and possibly even the wall. Current carrying...
Replies
6
Views
883
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Hello all, I wonder if I can get some opinion on my deliberations on an old TPN installation with numerous 1P sub-boards wired up with 16mm T&E...
Replies
5
Views
1K
I have a light switch where the CPC has been used for a lighting circuit and sleeved. Previously I would give this a C3 (411.3.1.1) and leave a...
Replies
11
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock