customer rings up ,I had a electrician round to put some sockets fronts in
the front room
and he told me you can use the sockets bar the socket for TV ,has no earth to it .
the spark is on holiday it had me think says the customer having no earth to the socket .
can you came and have a look ,turn up why did the spark not disconnect from the circuit I told the customer so you cant use it .
he also change the fuses from rewireble to those flick switches, you mean
wylex mcb yes
ok let me have a look at the socket and see why no earth.
holly F**K did the spark not tell you have VIR cable in that socket
and no earth sleeving .no said the customer.
I open the c/u most circuits had VIR cables on the lighting all sockets circuits
I'm afraid you need a rewire and a up grade of that old consumer unit
now the customer replays' back I have just move in weeks ago
cant afford a rewire.
where did you move from then, Yorkshire. mmmm. says it all .

.
 
customer rings up ,I had a electrician round to put some sockets fronts in
the front room.
and he told me you can use the sockets bar the socket for TV ,has no earth to it .
the spark is on holiday. it had me think says the customer having no earth to that socket .
can you came round and have a look ,turn up why did the spark not disconnect from the circuit I told the customer .so you cant use it .
he also change the fuses from rewireble to those flick switches, you mean wylex mcb yes.
ok let me have a look at the socket and see why you have no earth.
holly F**K did the spark not tell you have VIR cable in that socket
and no earth sleeving the customer said no.
I open the c/u most circuits had VIR cables on the lighting circuit all sockets circuits.
I'm afraid you need a rewire and a up grade of that old consumer unit
now the customer replays' back I have just move in weeks ago cant afford a rewire.
where did you move from then, Yorkshire. mmmm. says it all .!
is that ok
prospector-toy-story-11.png
 
Last edited:
there is actually a paragraph in approved doc P about VIR cables being beyond there service life.... handy if you get a customer that thinks your making it up because its been fine for 50 years yada yada!!!
 
About 10-12 years ago I actually did a CU change with all VIR cabling, couldn't believe it as they were like new and tested out perfectly, that's the only time though. It must have been the environment they were in or they were installed later than most.
 
The last few times I've seen it it has literally been crumbling with any bends. Only once in the last 10 year's have I seen it in good condition and I have to say it was good, wasn't working at it but had a quick look
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
star command
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Heavily Qualified Electrician / Teacher / Tutor - etc

Thread Information

Title
no earth to a socket
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
18
Unsolved
--

Advert

Thread statistics

Created
buzzlightyear,
Last reply from
Midwest,
Replies
18
Views
4,022

Advert

Back
Top