First thread guys so go easy on me.

I have recently finished a new installation and was having issues with the boiler room ring circuit tripping out the rcd. Put this down to earth leakage.

i wanted to know if I can make this a non-rcd protected circuit.

Problem is its not buried 50mm, is not surface run and has no metal conduit.

Any advice is appreciated.

cheers
 
First thread guys so go easy on me.

I have recently finished a new installation and was having issues with the boiler room ring circuit tripping out the rcd. Put this down to earth leakage.

i wanted to know if I can make this a non-rcd protected circuit.

Problem is its not buried 50mm, is not surface run and has no metal conduit
.

Any advice is appreciated.

cheers


did you..

find the fault and get it on an RCD...
 
Taking the circuit off the RCD is not the way. Find the fault; it's not that difficult.

Since this is a new installation, what were your IR readings for this circuit?

Taking this a little further, is this domestic or commercial? Type of earthing system?
 
hi im a new member here so hope to be of use and also to gain info in return sorry to barge in on your thread but can someone please guide me on how to start my own thread / question please
 
Taking the circuit off the RCD is not the way. Find the fault; it's not that difficult.

Since this is a new installation, what were your IR readings for this circuit?

Taking this a little further, is this domestic or commercial? Type of earthing system?


Its a domestic premises, tncs system. It tested out at greater than 500 ohms. R1 + R2 was fine, loop impedance was fine too.

It trips out intermittently, have looked through some other threads and people have had nuisance tripping due to earth leakage on loads that concern water e.g boilers, washing machine etc.

cheers
 
First thread guys so go easy on me.

I have recently finished a new installation and was having issues with the boiler room ring circuit tripping out the rcd. Put this down to earth leakage.

i wanted to know if I can make this a non-rcd protected circuit.

Problem is its not buried 50mm, is not surface run and has no metal conduit.

Any advice is appreciated.

cheers

Gasp!!!!!
 
Sorry I'm confused here, domestic, Boiler room ring circuit? How big is this house! So have you disconnected everything else on the ring to ascertain its the boiler at fault?
Have you wired the boiler and heating controls? Have you rechecked these connections are good and correct?
What if anything have you done to find fault?
Asumptions are not a technical get out for poor workmanship.
 
Its a domestic premises, tncs system. It tested out at greater than 500 ohms. R1 + R2 was fine, loop impedance was fine too.

It trips out intermittently, have looked through some other threads and people have had nuisance tripping due to earth leakage on loads that concern water e.g boilers, washing machine etc.

cheers



Is this a missprint?????
 
taking it from the RCD side of the board is a no no I would check the stat circuit to the boiler by this I mean the tank stat and room as they can trip rcds if a combi boiler the pump may be the issue you need to check this out as a starter
 
The RCD is tripping, so there is a fault somewhere, so your answer is to get rid of that pesky RCD?
 
Its a domestic premises, tncs system. It tested out at greater than 500 ohms. R1 + R2 was fine, loop impedance was fine too.

It trips out intermittently, have looked through some other threads and people have had nuisance tripping due to earth leakage on loads that concern water e.g boilers, washing machine etc.

cheers