The house is a good sized house with a 6ft by 6ft room housing all the central heating.

2 radials supplying immersions.
1 ring supplying 2 x combi boiler, pump and water softener.

All heating controls are wired by the companies heating engineer who assures me his wiring is all correct.

I have only just taken over from the previous supervisor 5 months ago. Before this I have always worked with someone. Still learning but this has got me scratching my head.

Have disconnected all loads and tested both radials and rthe ring. All test out fine, rcd tripping tests are within rang too.
 
Meant the ir came out at 500 mega ohms.

Will try and make sense of what I'm saying to you guys.

The central heating system consists of two radial circuits for immersions.
1 ring, on the ring, 2 boilers, 1 pump, 1 water softener.

with no loads connected to the circuit everything tests out fine.

the rcd can go for days without tripping and then trip. It seems to be when the heating system kicks in.

The heating engineer assures me that his wiring is all correct.

cheers
 
the rcd can go for days without tripping and then trip. It seems to be when the heating system kicks in.

How are the two combi boilers arranged? i.e., do they each serve a different part of the house or are they run in parallel, each contributing to the overall heating and hot water? Is it possible to electrically switch off/isolate one boiler and see if the fault persists or stops?
 
Meant the ir came out at 500 mega ohms.

Will try and make sense of what I'm saying to you guys.

The central heating system consists of two radial circuits for immersions.
1 ring, on the ring, 2 boilers, 1 pump, 1 water softener.

with no loads connected to the circuit everything tests out fine.

the rcd can go for days without tripping and then trip. It seems to be when the heating system kicks in.

The heating engineer assures me that his wiring is all correct.

cheers

its Meg....not Mega..

take no notice of `im...what does he know about our cables?......
 
the fault has to be on the connected load. the heating guy may be certain his wiring is OK, but a faulty component could be the culprit. has he made certain there's no water leaks?
 
If you are confident you have tested the fixed wiring and its OK, pass the problem to the heating engineer to fix his system as its faulty.

If you want to spend a bit more time and money, get your earth leakage clamp meter out and bring in the loads one at a time and measure leakage, there may be several leaky components so consider the total leakage of all, if you get anywhere near 15mA total your on for nuisance tripping.
 
If you are confident you have tested the fixed wiring and its OK, pass the problem to the heating engineer to fix his system as its faulty.

If you want to spend a bit more time and money, get your earth leakage clamp meter out and bring in the loads one at a time and measure leakage, there may be several leaky components so consider the total leakage of all, if you get anywhere near 15mA total your on for nuisance tripping.


Cheers, will have a word with the guy. Think it is a good idea to invest in a earth leakage clamp. Would know where I stand then.
 
your fault could be caused by a fault else where, not specifically the boiler circuit , if you have a N E short some where else in the installation but connected to the same RCD the boiler is connected to it could be causing the RCD to trip , it not always the obvious that causes the RCD to trip test the other circuits
 
How are the two combi boilers arranged? i.e., do they each serve a different part of the house or are they run in parallel, each contributing to the overall heating and hot water? Is it possible to electrically switch off/isolate one boiler and see if the fault persists or stops?

The combis run in Parallell of there own spurs so can seperately isolate them. Cheers
 
your fault could be caused by a fault else where, not specifically the boiler circuit , if you have a N E short some where else in the installation but connected to the same RCD the boiler is connected to it could be causing the RCD to trip , it not always the obvious that causes the RCD to trip test the other circuits

Have tested all the other circuits. I disconnected the boiler ring at the cu, including the neutral and earth. Did not get any tripping after this. This suggests to me it's on this ring.
 
the fault has to be on the connected load. the heating guy may be certain his wiring is OK, but a faulty component could be the culprit. has he made certain there's no water leaks?

Will ask him to look into this, to be honest I have never been involved with wiring for heating systems as always worked for this company and the heating engineer has always done his own wiring.

To be fair when I first started for the company I had to tell him that he must connect all his earths. He wasn't doing this before as he thought you didn't need to as the stats etc were plastic.
 
do a continuity test between N and E on the disconnected boiler circuit ,see what reading you get it may be nothing , be careful using IR tests on the boiler mind , what you could do is disconnect the boiler at the boiler and just power up the controlls
 
do a continuity test between N and E on the disconnected boiler circuit ,see what reading you get it may be nothing , be careful using IR tests on the boiler mind , what you could do is disconnect the boiler at the boiler and just power up the controlls

If you do any investigative IR testing at 250V, you'll be very unlikely to do any damage.
 
Looks like it was a pump on the central heating system. This was on a timer and was only tripping the rcd when the timer was switched on. Heating engineer has changed the pump and fingers crossed all seems fine. Cheers for all the help. Still gaining experience in fault finding!
 