The worrying point of this installation for the 11KV cables, is that MV cables don't like any areas of ''point pressure''. It can/will over time create a weakness at that point, where the higher voltage can penetrate the insulation to the semi conductive layer and on to the copper screening foils/tapes and beyond!! Seen this phenomena with MV/HV cables a good few times before. The problem is not so much the metal tray slightly penetrating the PVC over-sheath, it's the voltage trying to break through any weakness in the boundaries put in place to contain that voltage!! It's not as simple as your normal LV cable situations!!