Good morning all

Is there any reg to say about drilling cables into joists instead of notching?

I have been an electrician for 12 years now and have always drilled out timbers, we are starting a HUGGGGGGGGGGE rewire with long runs. It would save a lot of time i think to notch the top of the timbers and use a protective metal plate to go over after the install

Thoughts?
 
Notching is still acceptable, I’ve pulled this from the OSG for you.
Notching timbers instead of drilling.... image - EletriciansForums.net
 
The strength of a rectangular beam loaded in the vertical direction depends on the second moment of inertia I. Where I= B*D(cubed)/12 . Where B is the width of beam and D is the depth.
You need to know the exact dimensions but as an example: for a six-inch-deep beam with a one-inch- deep notch, the beam becomes effectively five inches deep. So, the original D(cubed) was 216 and the modified D(cubed) becomes 125. The strength is now 125/216 or 58% of the original.
For changes in stress levels, other factors such as distance from supports, are relevant.

For interest:
If you halve the width of a beam you reduce its strength by a factor of two.
If you halve the depth of a beam you reduce its strength by a factor of eight.
If you halve both width and depth you reduce its strength by a factor of sixteen.
 
The strength of a rectangular beam loaded in the vertical direction depends on the second moment of inertia I. Where I= B*D(cubed)/12 . Where B is the width of beam and D is the depth.
You need to know the exact dimensions but as an example: for a six-inch-deep beam with a one-inch- deep notch, the beam becomes effectively five inches deep. So, the original D(cubed) was 216 and the modified D(cubed) becomes 125. The strength is now 125/216 or 58% of the original.
For changes in stress levels, other factors such as distance from supports, are relevant.

For interest:
If you halve the width of a beam you reduce its strength by a factor of two.
If you halve the depth of a beam you reduce its strength by a factor of eight.
If you halve both width and depth you reduce its strength by a factor of sixteen.
Plumbers are exempt though! ;)
 
Personally I don’t notch beams. Over the years I’ve been unlucky enough to damage a few cables installed this method.

Someone has designed the beam to meet a load and as @ELECNEWT has mentioned notching will not help. Also, any top protection plate needs to be properly effective as any future damages or injury caused by penetrating the plate will be down to the installer, in my view. I haven’t seen a protection plate I trust so if I work on a circuit that has notching I re do it. This one was yesterday. Probably why I’m poor.

Notching timbers instead of drilling.... 7C5E18AB-8CB9-4E7C-994A-81DC36140394 - EletriciansForums.net
 
if. like me, you've worked on a load of terraced houses, top of stairs you often find a 3ft square "landing" between fron and rear bedrooms. the floor joists are 4" x 2" and as such drilling centre of joist ,cables will be <50mm from both surfaces. here, the only compliant option is to notch and plate.
[automerge]1596266761[/automerge]
Plumbers are exempt though! ;)
yes but plumbers do actually test the strength of the joist when notching out with an axe.
 
Last edited:
I never notch unless I have to. Personally my battery combi and self feed drill bits fly through joists in seconds. Notching would take much longer and wiring would require more daffy dressing with notches.

If I had a huuuuuge rewire to do I'd treat myself to something like the Milwaukee hole hawg ?
 
Mark up the joists perfectly in line before drilling and the cables will glide through from one end to the other.
except when the joists are too close together so you need to drill at a bit of an ange. in this case, my way is to drill first joist from 1 side, the next from the other side and so on alternate joist drilled left-right, right - left, etc. makes pulling a lot easier.
 
Been thinking about this , I’m thinking once a row of say 2 inch wide notches are cut into the joist , the cables can all be run and then simply laid into the notch. Then cover plates put over them.
If you had a lot of cables , laying them directly into a notch will be quicker than pulling in cables through holes one by one.

i still would opt for a row of 2 x 25mm holes
but that’s just me
 
Notching is allowed, but holes are preferable where possible.
I have notched joists in the past for running SWA or 16mm T&E because getting that stuff through holes ain't no fun sometimes.
 
Having notched and used holes... I reckon, if you're organised, it's far quicker with holes... would be fun to have a race !

A laser level, hole hawg and a combination square would be my weapons of choice.
 
Good morning all

Is there any reg to say about drilling cables into joists instead of notching?

I have been an electrician for 12 years now and have always drilled out timbers, we are starting a HUGGGGGGGGGGE rewire with long runs. It would save a lot of time i think to notch the top of the timbers and use a protective metal plate to go over after the install

Thoughts?
Notching over holes wins hands down. And laying the cables in rather than pulling through holes in joists is, nt just a great time saver, it's kinder on the cable Insulation. My only problem with it is I don't get to "notch" often enough. Ideally I try to first fix before the upstairs flooring goes down. In agreement with the builder I " notch" the joists where they are resting on a stud or wall. I never do it otherwise. To avoid waking joists
[automerge]1596396290[/automerge]
Notching over holes wins hands down. And laying the cables in rather than pulling through holes in joists is, nt just a great time saver, it's kinder on the cable Insulation. My only problem with it is I don't get to "notch" often enough. Ideally I try to first fix before the upstairs flooring goes down. In agreement with the builder I " notch" the joists where they are resting on a stud or wall. I never do it otherwise. To avoid waking joists
Sorry "weakening"
 

Reply to Notching timbers instead of drilling.... in the Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock