Thought I was onto a real winner today when checking the gas bond to find a nice bonding conductor run directly to a local earth rod:

2020-09-28 15.06.50.jpg


The main house is currently TT with a rod on the opposite side of the house, so maybe they thought the foundations counted as a massive MET :rolleyes:

Was all set to run cabling round the house, but as it happens, further testing between the MET and this showed very low resistance (boiler cpc was my first guess), and when I delved into the CU there was a 10mm bonding conductor which goes maybe to the boiler in the attic, and gives a reading of 0.04 back to this pipe.

Means their current earth is effectively the gas pipe rather than either rod though, since Zs on my new lights outside is 2Ohmish, while Ze was 193...

DNO visit in a week or so hopefully will upgrade to PME.

Any reason electrically to remove this connector? Might stop the next guy thinking the same, though I will put a sticker inside the box or at the CU to clarify I think.
 
Yes, someone who totally missed the concept of equipotential bonding!

Given the good internal bond it is not really an issue, but as you say it ought to be documented or tidied up so no one gets confused in the future.
 
Yes, someone who totally missed the concept of equipotential bonding!

Given the good internal bond it is not really an issue, but as you say it ought to be documented or tidied up so no one gets confused in the future.
I did check rod to rod just to be sure, but many ohms difference of course...

Goes to show that testing bonding is sometimes beneficial though - Before I got my wander lead I would likely have just run a new one...
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Dartlec

Arms
Joined
Location
Kent
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)
Business Name
Dartlec

Thread Information

Title
Novel gas main bonding
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
2
Unsolved
--

Advert

Thread statistics

Created
Dartlec,
Last reply from
Dartlec,
Replies
2
Views
946

Advert

Back
Top