Hi all, Do you guys and girls make observations on the fire detection when you do an EICR? If so how do you code it? I've always observed shortfalls in fire detection on an EICR and coded it seperately as 'FIRE' but I was chatting to another sparky the other day who incorporates his fire detection obs into the normal C1, C2, C3, FI coding system. What's your opinion?
 
Instyle LED Lighting Specialists UK
This official sponsor may provide discounts for members

UNG

-
Mentor
Esteemed
Arms
Reaction score
2,686
Hi all, Do you guys and girls make observations on the fire detection when you do an EICR? If so how do you code it? I've always observed shortfalls in fire detection on an EICR and coded it seperately as 'FIRE' but I was chatting to another sparky the other day who incorporates his fire detection obs into the normal C1, C2, C3, FI coding system. What's your opinion?
What is he coding if it's the mains wiring ok anything else is really out of the remit of an EICR other than maybe a comment on the age of the detectors
 

Darkwood

Mod
Mentor
Esteemed
Arms
Reaction score
9,875
As above the EICR is an inspection of the electrical installation in regards to its safety and its compliance either to the time it wa installed if not a safety concern or to modern regulations, unless the BS7671 stipulates in its regulations what you are covering with these extra comments then it can only be done as a separate observational point/ recommendation additional to the EICR and not part of it.
 

Lister1987

-
Trainee
Esteemed
Reaction score
852
Any non-compliances with 5839-1 (or -6) can be noted against 560.10.

Being that a fire detection system is a life safety system, any obvious nonconformities that DON'T hinder the system operation I would attract a C2, any that did affect system operation would be a C1, on the basis that if the system isn't to standard or working then you would not be able to Guarantee operation as intended.

SparkyNinja/e5 did an interesting vid on EICRs that encounter fire alarms, worth a watch.
 

Flanders

-
Esteemed
Arms
Reaction score
829
I have mention on EICRs if a mains powered smoke detector is damaged or missing and wrote it down as info on the report. I would only code it if it was electrical unsafe ( if there was exposed live parts for example) as others have said there is no requirement in an EICR to confirm the fire alarm is working correctly. If the property is rented i believe it is requirement that the smoke detector are inspected annually but that would be on a separate report.
 

Flanders

-
Esteemed
Arms
Reaction score
829
Any non-compliances with 5839-1 (or -6) can be noted against 560.10.

Being that a fire detection system is a life safety system, any obvious nonconformities that DON'T hinder the system operation I would attract a C2, any that did affect system operation would be a C1, on the basis that if the system isn't to standard or working then you would not be able to Guarantee operation as intended.

SparkyNinja/e5 did an interesting vid on EICRs that encounter fire alarms, worth a watch.
Not sure you could give it code 1 . As a code 1 constitutes an immediate danger, there will only be a dangerous situation if the building catches of fire and the smoke alarm does not inform the occupier. So that would be a potential danger. You do have a good point about reg 560.10. Though
 

Lister1987

-
Trainee
Esteemed
Reaction score
852
Not sure you could give it code 1 . As a code 1 constitutes an immediate danger, there will only be a dangerous situation if the building catches of fire and the smoke alarm does not inform the occupier. So that would be a potential danger. You do have a good point about reg 560.10. Though
I know it doesn't meet the ethos behind C1 (I can see it, I can touch it, it will kill me now) but as a C2 would have the desired effect it's rare a C1 would be issued, such as cover missing from the FCU Spur and so live parts being visible.
 

UNG

-
Mentor
Esteemed
Arms
Reaction score
2,686
Any non-compliances with 5839-1 (or -6) can be noted against 560.10.

Being that a fire detection system is a life safety system, any obvious nonconformities that DON'T hinder the system operation I would attract a C2, any that did affect system operation would be a C1, on the basis that if the system isn't to standard or working then you would not be able to Guarantee operation as intended.

SparkyNinja/e5 did an interesting vid on EICRs that encounter fire alarms, worth a watch.
Noted is slightly different to coding a non conformity with BS5839 beyond the wiring how far do you go into BS5839-6 system and beyond the scope of the BS7671 inspection you are employed to do

Do you confirm any radio links are functioning correctly do you check the sound levels at the bed head comply with the requirements while you are there as well

I would like to know how you would handle a commercial EICR with a BS5839-1 system installed
Also how many BS5839-6 systems have you coded with a C1 or C2 while doing EICR's

TBH a lot of these videos are not worth a watch and are not even worth the bandwidth they take up
 

Lister1987

-
Trainee
Esteemed
Reaction score
852
Noted is slightly different to coding a non conformity with BS5839 beyond the wiring how far do you go into BS5839-6 system and beyond the scope of the BS7671 inspection you are employed to do

Do you confirm any radio links are functioning correctly do you check the sound levels at the bed head comply with the requirements while you are there as well

I would like to know how you would handle a commercial EICR with a BS5839-1 system installed
Also how many BS5839-6 systems have you coded with a C1 or C2 while doing EICR's

TBH a lot of these videos are not worth a watch and are not even worth the bandwidth they take up
This is where the knowledge of the inspector (and any prior agreements with client) would decide exactly how far one goes.

I wouldn't go deliberately looking for 5839 deviations but any obvious ones that would make me question the efficiency of the system would get a C3 and further noting about getting a service done to correct any deeper issues.

As an electrician you could only code what you could see, if however you also had working and sufficient knowledge of 5839-1 to do what equates to a handover inspection (you're taking over a system from another provider so you do your own inspection noting system makeup etc), but if that person had such knowledge and was ethically switched on enough to include enough in the report to highlight the issue but not so much as to give away a complete service, then I would have no issue with it at all.
 

loz2754

-
Esteemed
Arms
Reaction score
1,505
Coding for deficiencies in a BS5839 would only be covered by a full inspection and test of the fire detection and alarm system. As such, there is no place for coding C1, C2 or any other code for such a system, other than what is covered by BS7671.
 

Lister1987

-
Trainee
Esteemed
Reaction score
852
Coding for deficiencies in a BS5839 would only be covered by a full inspection and test of the fire detection and alarm system. As such, there is no place for coding C1, C2 or any other code for such a system, other than what is covered by BS7671.
Unless you have sufficient knowledge and can back up your coding, even if only as a C3 (to bring it to user attention) with the relevant clauses. Example;

Property has mixed styles of Manual Call Point; both older style with for circular break glass and newer BS EN 54-11, contrary to 5839-1 Clause 20.2a

Property has call points lacking protective cover, contrary to 5839-1 Clause 20.2b

and so on.

Obviously if you don't have knowledge of 5839-1 (and any of the standards in 560.x) then you shouldn't be coding those item, in which case you are working within the limits of your knowledge and understanding. If you were to find such issues then you would strongly recommend that the client seeks the advice of a trained and competent person to undertake a system audit, inspection and maintenance program.

I'm seen 1 where the EICR was done, flagged several C3s for 1838/5266 & 5839 shortcomings then accompanying the EICR was a full diagnostic report of systems, shortcomings and recommendations to improve complaince.

I'm not saying it's for everyone but we should always look to better ourselves, our skillsets and services offered to drive value for money and to seperate us from the beasts....and by beasts imwan DIY Dave and Bodge-it Brenda.
 