Discuss Odd problem with Fan belts on extract fan. in the Commercial Electrical Advice area at ElectriciansForums.net

D

Denatone

This situation has happened at work and I'm wondering if anyone has come across anything similar because i'm a little stumped.

Came in to find HVAC system wasn't running as the BMS was recording an airflow failure in the extract part.
Large belt driven impeller extract fan for the building run from star/delta starter.
Check the control circuit and power circuit for the starter system and the 63A BS88-2 fuses (gG not gM for some reason) in two of the phases had blown.
Check continuity and IR down motor windings everything looks normal
Replace fuses and the motor seems to start and run fine but the BMS is still saying no flow.
Actually physically check the motor and drive-shafts and find that the 3 belts connecting motor to impeller shaft have come off the pulley, not snapped just come off and 2 have big chunks taken out. (spb 4250 belts so not exactly small)
Inspected the shaft, the safety enclosure and the impeller and both are fine and undamaged.

Any ideas as to what caused them to come off and would them coming off cause a sudden increase/decrease in the load that would cause the motor fuses to blow?

Cheers
 
.........Any ideas as to what caused them to come off and would them coming off cause a sudden increase/decrease in the load that would cause the motor fuses to blow?

Cheers
9 times out of 10 belts would derail off the pulleys due to lack of maintenance. Especially with longer belts they need periodically tensioning to take up the slack and obviously replacing if they show signs of wear and tear. Quite often if they get too slack a single one of the belts derails and it gets dragged around the pulley wheels at high speed by the remaining belts which then also get derailed so it's normal to find that either all the belts are still on or all the belts are off and hence they look like they've been through a war zone.

If you purchase new belts try and get the suppliers to match them as close as possible for length, it makes life easier for setting them up on the fan. When you install them just check the shafts and the pulley wheels are still straight and obviously check the geometry between the two pulley wheels is correct....and don't over tighten them otherwise you'll be replacing bearings next week!!!!!

As for taking out fuses, if the motor tests good and is still running smoothly ie no mechanical damage, the only reason I can imagine is that the derailed belts got tied up around the motor pulley and caused overload or locked rotor. During overload conditions one of the fuses will win the race and immediately the current on the remaining two phases will increase rapidly until a second fuse blows. At this point the current on the remaining phase drops to zero because there's no return path so the third fuse remains in tact.
 
Yeah that sounds about right. It had me and the boss scratching our heads about it.
Mostly trying to work out if the motor failed and somehow threw the belts or the belts came off and that somehow blew the fuses.
cheers for that i'll make sure the new belts go on proper
 
Make sure the transition time on the SD starter is set correctly. Too long or too short and it will reduce the lifetime of the belts with undue loading.
 
Think Marvo's kind of nailed this on the head and put it to bed ... the fuses blowing is a little bit of a curve ball TBH but plausible as we don't really know what could have shot the current up so fast that the fuses were taken out rather than the overload protection (check this is set up correctly 0.58 x FLC if in Delta leg)... but yes as marvo says it could have locked the rotor long enough if the belts jumped off and jammed between the pulley and housing.
 
PS.... I'd be inclined to check manually and electrically the shaft for smooth rotation it could be the case a cracked ball bearing may have locked the rotor jumping the belts off as a consequence, this may have freed itself but could be evident by listening and feeling the shaft while turning it.
 
Last edited:
As DW rightly added it's worrying that the thermal overload protection should have picked up the fault and tripped before the fuses let go unless the fuses are very closely rated compared to the run current. I'm assuming there is a thermal overload if the fuse type is gG and not aM type. The fact the fuses blew would certainly warrant checking the thermal overload is operational and is correctly set on the current selector and also make sure the thermal isn't set to auto re-close after fault disconnection.

*Edit*
One other thought occurred, it's a long shot but I encountered a large (37kW) forward curved centrif fan many years ago that used to throw belts sometimes when they periodically tested the mechanical fire dampers. When the dampers slammed closed the sudden change in load caused problems. Some fans are more susceptible to overloading under increasing static pressure than others, it's doubtful you'd ever encounter a similar problem with a backward curved fan for example.
 

Reply to Odd problem with Fan belts on extract fan. in the Commercial Electrical Advice area at ElectriciansForums.net

Similar Threads

Hi don’t know if anyone can help. Starter motor for a countax ride on lawnmower K14 1992 briggs and Stratton vanguard 14hp engine 2 months ago...
Replies
17
Views
7K
Hi Guys Got a full refurb job coming up which includes x3 first floor bathrooms, each to have extraction. Currently have priced 1 x 4" wall...
Replies
13
Views
4K
I'm looking at a German made roller conveyor system 10 motors contactors controlled by a PLC Issue is customer says 3 mths ago motors started...
Replies
23
Views
3K
I hear many views of people who believe that DPF's and CDPF's fitted to their vehicles are a problem and many people resort to removing them, or...
Replies
0
Views
8K
Apologies up front for the long post. I thought I'd try to include as much info as I can. I am looking for some advice/suggestions any of you...
Replies
12
Views
21K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock