D
Denatone
This situation has happened at work and I'm wondering if anyone has come across anything similar because i'm a little stumped.
Came in to find HVAC system wasn't running as the BMS was recording an airflow failure in the extract part.
Large belt driven impeller extract fan for the building run from star/delta starter.
Check the control circuit and power circuit for the starter system and the 63A BS88-2 fuses (gG not gM for some reason) in two of the phases had blown.
Check continuity and IR down motor windings everything looks normal
Replace fuses and the motor seems to start and run fine but the BMS is still saying no flow.
Actually physically check the motor and drive-shafts and find that the 3 belts connecting motor to impeller shaft have come off the pulley, not snapped just come off and 2 have big chunks taken out. (spb 4250 belts so not exactly small)
Inspected the shaft, the safety enclosure and the impeller and both are fine and undamaged.
Any ideas as to what caused them to come off and would them coming off cause a sudden increase/decrease in the load that would cause the motor fuses to blow?
Cheers
Came in to find HVAC system wasn't running as the BMS was recording an airflow failure in the extract part.
Large belt driven impeller extract fan for the building run from star/delta starter.
Check the control circuit and power circuit for the starter system and the 63A BS88-2 fuses (gG not gM for some reason) in two of the phases had blown.
Check continuity and IR down motor windings everything looks normal
Replace fuses and the motor seems to start and run fine but the BMS is still saying no flow.
Actually physically check the motor and drive-shafts and find that the 3 belts connecting motor to impeller shaft have come off the pulley, not snapped just come off and 2 have big chunks taken out. (spb 4250 belts so not exactly small)
Inspected the shaft, the safety enclosure and the impeller and both are fine and undamaged.
Any ideas as to what caused them to come off and would them coming off cause a sudden increase/decrease in the load that would cause the motor fuses to blow?
Cheers