I'm looking at a German made roller conveyor system 10 motors contactors controlled by a PLC

Issue is customer says 3 mths ago motors started stopping and overheating, and would then start again when cooled down
Overloads trip out PLC, input switches contactors off and someone presses reset
(It's a year old, the maintenance team are mechanical bias)

So as this was sold by our firm we are first to check
1st thing I notice is panel is warm, open it and hot plastic smell comes out
I felt the contactors and where they connect to Overloads it's pretty warm, and a slight melting off a small area on the top of the overloads, where the self maintaining contacts are snapped off
obvious issue here

So I turn it off check all the connections are tight, some weren't as tight as I think they should be but no loose connections

So I start turning motor circuits off to check continuity and resistance through all components , voltage at all terminals except motor as it's not safe to do this tested / inspected everything I can think of even recorded temperature of motors and the components in the board, bench tested one of the motors all good
nothing untoward found, all current readings at @ 0.6 A motor plate says 0.9 A , O/L's set at just over 1 A

So I'm checking how it's running sensors actuating contactors etc and noticed occasionally when the line builds up due to downstream conveyors being stopped by staff, that the contactors are being turned on and off very quickly with the result the motor is getting hot as fan isn't running enough air over the casing to cool it, normal running its fine
Asides from the suspect overloads and this timing issue all looks good

Yesterday I smelt a hot motor it was single phasing checked O/L and found a phase down
Removed it opened up and one of the filaments is open circuit

I report back to German Engineer he says he agrees with the timing issue but he doesn't agree with my request for new overloads to be sent even after seeing the broken one

I sent him all readings and photos etc
He's still adamant it must be a supply voltage issue or something else that I have missed as this is a small simple system
And they have built lots of these with no issues
So I'm still onsite monitoring things

So just wanted to see if others have any opinions or ideas
[automerge]1580903734[/automerge]
Burnt plastic connecting the two self maintain contacts
[automerge]1580903799[/automerge]
Open circuit filament
 

Attachments

  • IMG-20200204-WA0013.jpeg
    IMG-20200204-WA0013.jpeg
    40.3 KB · Views: 29
  • IMG-20200204-WA0017.jpeg
    IMG-20200204-WA0017.jpeg
    89 KB · Views: 30
Last edited:
I'm looking at a German made roller conveyor system 10 motors contactors controlled by a PLC

Issue is customer says 3 mths ago motors started stopping and overheating, and would then start again when cooled down
Overloads trip out PLC, input switches contactors off and someone presses reset
(It's a year old, the maintenance team are mechanical bias)

So as this was sold by our firm we are first to check
1st thing I notice is panel is warm, open it and hot plastic smell comes out
I felt the contactors and where they connect to Overloads it's pretty warm, and a slight melting off a small area on the top of the overloads, where the self maintaining contacts are snapped off
obvious issue here

So I turn it off check all the connections are tight, some weren't as tight as I think they should be but no loose connections

So I start turning motor circuits off to check continuity and resistance through all components , voltage at all terminals except motor as it's not safe to do this tested / inspected everything I can think of even recorded temperature of motors and the components in the board, bench tested one of the motors all good
nothing untoward found, all current readings at @ 0.6 A motor plate says 0.9 A , O/L's set at just over 1 A

So I'm checking how it's running sensors actuating contactors etc and noticed occasionally when the line builds up due to downstream conveyors being stopped by staff, that the contactors are being turned on and off very quickly with the result the motor is getting hot as fan isn't running enough air over the casing to cool it, normal running its fine
Asides from the suspect overloads and this timing issue all looks good

Yesterday I smelt a hot motor it was single phasing checked O/L and found a phase down
Removed it opened up and one of the filaments is open circuit

I report back to German Engineer he says he agrees with the timing issue but he doesn't agree with my request for new overloads to be sent even after seeing the broken one

I sent him all readings and photos etc
He's still adamant it must be a supply voltage issue or something else that I have missed as this is a small simple system
And they have built lots of these with no issues
So I'm still onsite monitoring things

So just wanted to see if others have any opinions or ideas
[automerge]1580903734[/automerge]
Burnt plastic connecting the two self maintain contacts
[automerge]1580903799[/automerge]
Open circuit filament
What are the voltage parameters stated on the Motors and what voltage are you supplying the machine with?
Is the conveyor system maintained properly and is it Mechanically overloaded at any stage, causing the motors to overheat due to over working?
 
  • Agree
  • Like
Reactions: Dabbers and edexlab
400v 3~
Checked gearboxes, listened to them ,temps and turned all by hand nothing except for a very slight leak of oil on one gearbox

Maintenance team not experienced electrically, they try their best I think....

As I said the contactor switching rapidly when there is a build up of boxes causes the motors to heat up, the conveyors affected most of the time are short and can only carry a couple of boxes which are well within the motors capability
 
Contactors and motors are only expected to do a certain amount of starts before they have worn out or burnt ou the contacts.
Also they are often only expected by the manufacturer to do so many starts per hour.

If they have been starting and stopping very fast for some time, they may well have reached there end of life.

Check manufacturer data sheet for the info.
 
  • Agree
  • Like
Reactions: marconi and edexlab
I'm thinking it's a straightforward thing
Replace hot and heat damaged overloads as one has already failed
Change PLC program to give a longer delay to ensure there aren't too many boxes on conveyor at any time and then monitor temperature in the panel and motors to see if the heat is a symptom or the cause

But the German guy is saying there must be another issue and won't accept that the Overloads could be the cause, ie whether caused by connections/ bad batch , says its impossible....
 
400v 3~
Checked gearboxes, listened to them ,temps and turned all by hand nothing except for a very slight leak of oil on one gearbox

Maintenance team not experienced electrically, they try their best I think....

As I said the contactor switching rapidly when there is a build up of boxes causes the motors to heat up, the conveyors affected most of the time are short and can only carry a couple of boxes which are well within the motors capability
Understand you saying the Mechanical engineers aren't biased to the Electrical side of things, but not maintaining something that is relying on an Electrically driven Mover can and does sometimes cause stress to the Mover in this case the Motor and it's associated control gear.
 
  • Agree
Reactions: edexlab
Yes checked switching ratings of contactors
These are standard components for this firm
As said before this company builds big and complex systems usually longer than this a
 
I'm thinking it's a straightforward thing
Replace hot and heat damaged overloads as one has already failed
Change PLC program to give a longer delay to ensure there aren't too many boxes on conveyor at any time and then monitor temperature in the panel and motors to see if the heat is a symptom or the cause

But the German guy is saying there must be another issue and won't accept that the Overloads could be the cause, ie whether caused by connections/ bad batch , says its impossible....
No good changing the overloads just because they are getting warm, first step is to find out why They are getting warm, otherwise the same may happen to the replacements.
 
No good changing the overloads just because they are getting warm, first step is to find out why They are getting warm, otherwise the same may happen to the replacements.

Agree 100% and have been constantly checking things for 2 days , not seen anything unusual at all

As I said before after all checks the Overloads that have tripped have done so when it's set at just over 1 A,
I've had clampmeters on and watched and it's never gone above the running current approx 0.6A

Admittedly I only have two clampmeters available so I've checked two phases and alternated between them to try and catch a higher reading, requested a third one ....
 
Also when the overload failed there were no spares, so as a test ran it directly off the relay for a few hours until got a replacement, monitored the current / voltage to see if the motor was behaving and not seen anything strange, so to me it points back to the overloads again,
 
Agree 100% and have been constantly checking things for 2 days , not seen anything unusual at all

As I said before after all checks the Overloads that have tripped have done so when it's set at just over 1 A,
I've had clampmeters on and watched and it's never gone above the running current approx 0.6A

Admittedly I only have two clampmeters available so I've checked two phases and alternated between them to try and catch a higher reading, requested a third one ....
Rather than do that hire a supply monitor and leave connected for a period of time
 
It was just to keep them going but also I think its shown that the motor may be ok
I have 2 new overloads fitted spaced all of them so there is an air gap , set it slightly below rated current, and in manual reset

Part of the problem is the overloads were set to auto reset and when they first had problems here they just pressed the master reset and carried on until it happened again, no investigation into why it was stopping .
[automerge]1580912439[/automerge]
I've asked them to get supply monitored also
 
It was just to keep them going but also I think its shown that the motor may be ok
I have 2 new overloads fitted spaced all of them so there is an air gap , set it slightly below rated current, and in manual reset

Part of the problem is the overloads were set to auto reset and when they first had problems here they just pressed the master reset and carried on until it happened again, no investigation into why it was stopping .
[automerge]1580912439[/automerge]
I've asked them to get supply monitored also
Nothing much more you can do at present other than keep an eye on things and await the delivery and installation of the monitor is there.
 
  • Like
Reactions: edexlab
You say the machine's a year old...….surely it's still under some warranty with the suppliers, from your point of view. I would have thought they'd have maintenance engineers at the ready if it's that new.
How much did it cost? If there are 10 motors involved, it must decent sized.
Your firm must have come across problems before.
 
  • Agree
Reactions: Pete999
This is third party equipment sold as a package for complete system,

My company (Dutch) builds the main machine, that feeds product to the conveyor I work for UK service dept, this conveyor is built in Germany
I'm here as first response to the warranty, as the OEM is abroad its easier for us to attend first

They're sending a Senior Engineer today
However it's been running fine today no stops for 6 hrs so far which they haven't had for several weeks usually runs for between 30mins and 2 hrs before its stopping
 
You say the machine's a year old...….surely it's still under some warranty with the suppliers, from your point of view. I would have thought they'd have maintenance engineers at the ready if it's that new.
How much did it cost? If there are 10 motors involved, it must decent sized.
Your firm must have come across problems before.
Could be, the Machine has been incorrectly specified from day 1.
 
Possible but it looks modular ie add sections to make bigger system, I've seen other systems they have done and they look identical
 
This is third party equipment sold as a package for complete system,

My company (Dutch) builds the main machine, that feeds product to the conveyor I work for UK service dept, this conveyor is built in Germany
I'm here as first response to the warranty, as the OEM is abroad its easier for us to attend first

They're sending a Senior Engineer today
However it's been running fine today no stops for 6 hrs so far which they haven't had for several weeks usually runs for between 30mins and 2 hrs before its stopping
Fair enough. You seem to have got there, to some degree.
It just seems a bit pointless asking on the forum when you are part of the maintenance team. You probably know more about the unit than the rest of us put together.;)
 
I don't usually work on this equipment but it's just a conveyor with motors so nothing special
The point of the thread is that I think I have found the problem and tested/ investigated any possible causes all of which have pointed back to the same thing,

I'm still relatively new to Automation having learnt as I go and am looking for anything I might have missed that can be checked

Another more qualified engineer ( German) has cast doubt on my findings even though he's actually complimented me on how I recorded all the details
and to me is ignoring the facts to the point he's sending a guy here to check for supply problems
 
  • Like
Reactions: DPG and ipf
I'm still relatively new to Automation having learnt as I go and am looking for anything I might have missed that can be checked

Another more qualified engineer ( German) has cast doubt on my findings even though he's actually complimented me on how I recorded all the details
and to me is ignoring the facts to the point he's sending a guy here to check for supply problems
Geeermans!……...I had one on the phone from the Fatherland, years ago, telling me I was wiring star delta starters wrong on some new spray booths, they were tripping on changeover. It was a load issue. I'd temporarily upgraded the starters without them knowing (client didn't want them to) and they were working perfectly. Faxing drawings to show me how to wire 'em……..cheeky b**ger.
 
Last edited:
I actually like most of the Germans I've met and like the way they live in the South of the country, I think they still have good values and lifestyle there

Don't understand the shouting though!!!

I've just spoken to him he is back pedaling now asking if I still think the Engineer should come or not.......

I only asked them to send a few parts not an Engineer

Maybe something got lost in translation he says,

But his English is better than mine and that's only because he has a German accent!

Guys on the way to the Airport now I spoke to him he is coming anyway as he wants to look at the site for the next machine installation
Apparently it's his Dad that's coming
He's the owner of the company!
 
  • Like
Reactions: ipf
Geeermans!……...I had one on the phone from the Fatherland, years ago, telling me I was wiring star delta starters wrong on some new spray booths, they were tripping on changeover. It was a load issue. I'd temporarily upgraded the breakers without them knowing (client didn't want them to) and they were working perfectly. Faxing drawings to show me how to wire 'em……..cheeky b**ger.
Correction Upgraded the breakers.
 
Check that the contractors are correctly rated for switching of motors under load, (AC3/AC23) I have found panel builders use the wrong componanrts.
As the overloads are thermal the heat from the contactors can cause problems, you could use remote mountings for the overloads to move them away from the contactors.
 
  • Like
Reactions: James
Ok bit of an update
Yesterday 2 new overloads fitted didn't have any stoppages all day until the conveyor got jammed ( that's another issue being dealt with)

I'd just checked the relay and overload voltage and continuity, current and temperature etc as I was keeping tabs on it

Cleared the jam gave it a few minutes to cool and switched back on again

I noticed the solenoid lever went across as normal then after a second or two it moved a few mm to the right, this hadn't happened before
Looked like it was on but clamp meter told me it was fluttering so I checked the coil which was ok but the contacts were starting to change colour from heat and some arcing spots were visible, I compared it to one next to it which was switching slightly less than this one, big difference in appearance

So I think instead of the usual story of arriving and something had failed,

I got to see the problem while it was failing

German Engineer agreed with me today after checking things through himself that that the PLC needed a longer delay between switching and he is going to trial some higher duty relays here and if it proves reliable change the spec on his conveyor systems with the same spec as this

He said normally their systems are several hundred metres with upto 200 motors but as these are longer, there is less switching of motors as there are buffer areas preventing more than 3 boxes on any section at any time
 
  • Like
Reactions: marconi

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

edexlab

Arms
~
Joined
Location
Uk
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Electrical Engineer (Qualified)

Thread Information

Title
Overload issue
Prefix
N/A
Forum
Electrician Forum
Start date
Last reply date
Replies
23

Thread Tags

Advert

Thread statistics

Created
edexlab,
Last reply from
edexlab,
Replies
23
Views
3,269

Advert