I'm hoping someone can sanity check or correct my thinking. I have a very old UPS, it's showing a power factor on the front display of 0.1
We put a clamp meter on the 3 incomers which all read 36 Amps. the 3 outgoing legs are showing 12, 6 and 4 Amps
That's 108 Amps in and 22 Amps out, I'm wasting 86 Amps?
86Amps is roughly 20kW x 24Hrs x 365Days x 35p/kWh = £61K
Am I really burning £61K?
My plan is to replace this relic with a modern smaller UPS but want to be able to confidently say to my boss that I'm spending £10K on a new UPS and will save £61K.
TIA