What sort of earthing system is it ?
It's Friday night and I started early.... but I'd say still TN-C-S really, Just the S is happening at the CPC bar not the cut-out.
The neutral is disconnected from the meter, so when the switch is open there is only one neutral conductor and that's the same one as the cpc,
completey agree
where is the separation of the cpc and neutral ?
The CPC bar. The main earth arrives there which is being misused as a PEN conductor. Imagine the G/Y conductor going to the main switch is blue. We don't have to agree! It's a crazy setup after all. But I think the RCDs would work.
 
Do you think L to Cpc would trip the rcd ? or mcb ?
Yes. Forget the RCD a minute. If current can flow from the MCB through a load and back via the N bar, via the RCD, and the load works, then we've proved it's possible for current to flow. Lower the resistance, all the way to negligable if you like, and lots of current will flow, the and MCB will trip. Or has the 1664 completely broken my brain?

For the RCD, anything that goes through it on the L side and doesn't come back on the 'other pole' will cause an imbalance and it will trip.

If you take the meter completely out of the installation and forget it, this is electrically equivalent to every TN-C-S install. Just the point where PEN becomes N and CPC has shifted but it's still upstream of the RCDs.
 
Yes. Forget the RCD a minute. If current can flow from the MCB through a load and back via the N bar, via the RCD, and the load works, then we've proved it's possible for current to flow. Lower the resistance, all the way to negligable if you like, and lots of current will flow, the and MCB will trip. Or has the 1664 completely broken my brain?

For the RCD, anything that goes through it on the L side and doesn't come back on the 'other pole' will cause an imbalance and it will trip.

If you take the meter completely out of the installation and forget it, this is electrically equivalent to every TN-C-S install. Just the point where PEN becomes N and CPC has shifted but it's still upstream of the RCDs.
I need a holiday ....
 
How would you stop the neutrals from acting as proper neutrals though since they're all physically connected correctly in the board?

I'm trying to visualise a set up whereby the board can look normal but can be switched to use earth as neutral.
There are two large diameter cables going from the CU to the same point in the head, a blue and a green yellow. The blue passes through the meter and the other doesn't, swapping them won't affect the installation because they're joined anyway, essentially it's just a cable colour changing crossover switch.

The CSA is different 16mm-25mm if you're fussy , but if the deteriorating rubber DNO tails to the meter are 10mm anyway I can't see it being an issue
 
There are two large diameter cables going from the CU to the same point in the head, a blue and a green yellow.
No there isn’t the blue conductor isn’t connected to the meters neutral as the incoming to the meter has been disconnected, leaving a switched shared cpu/neutral connected to the meters output.
 

Reply to On the fiddle ______________ in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hello, Looking for some advice following a botched 3 phase upgrade today. Some background: Commercial unit originally fitted out (4 years ago)...
Replies
7
Views
681
Just interested in peoples thinking on using the neutral through the earthing system like I came across today. I've come across many wrong...
Replies
10
Views
2K
Hi. Can anyone offer a bit of advice please. I've got a customer who wants needs an upgrade to their consumer units. It is a bungalow that has a 3...
Replies
11
Views
7K
Over the last few days, I have stumbled across a number of threads that seem to point to a prevalent misunderstanding. Either that, or I have been...
Replies
6
Views
2K
Whew makes me wonder if a part P inspection should be part of the house move process! The house I have moved into is a nightmare, I thought...
Replies
73
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock