Thats what I thought but was more concerned with using a single conductor to combine N and Cpc I would have thought could upset an rcd.

Residual current devices (RCD) rely on detecting currents flowing in the earthing conductor by measuring the out of balance currents between phase and neutral conductors. In a TN-C installation, the neutral and earthing conductor are combined, thus making the detection of residual current impossible.

You cannot tell what is a legitimate neutral current, and what is an earth fault current using the PEN, as the earth and neutral combined.
 
Last edited:
In a TN-C installation, the neutral and earthing conductor are combined, thus making the detection of residual current impossible.
I don't think it's helpful to label this installation as a TN-C. I understand that in some ways that is correct, but it is causing confusion.
In a true TN-C system there wouldn't be an N or a CPC for any of the loads, just a PEN. In a true TN-C setup earth faults are indeed impossible to detect using an RCD.
1687801581635.png

In this installation, the neutral and earthing of loads are separated. The loads have N connected to the RCD and the CPC connected to the CPC bar. In turn, the CPC bar is connected to the N incomer on the main switch.
Therefore any current flowing through the CPC will not pass back through the RCD and the RCD will trip due to the imbalance.

1687801977434.png
Apart from the colour of the wire, I maintain that it is electrically exactly the same as this:
1687802117614.png

Discuss!
 
Last edited:
I cant find a ~100a version of the crossover switch in the picture, one that will link straight through L-R and then when turned join L green to R blue as well as L blue to R green. It's easy enough to do in electronics but I guess no-one makes an electric sized version. Sorry for the floppy CAD, turns out windows paint 3D is ----
 

Attachments

  • crossover.jpg
    crossover.jpg
    84.3 KB · Views: 12
In a meter the neutral plays no part in the measurement unless its used to power (with the line) any electronics present in the meter .
i have taken single phase meters apart and there is always a solid neutral link with the live sent though a current shunt , the volt drop is then measured over the shunt to calculate amps
 
I cant find a ~100a version of the crossover switch in the picture, one that will link straight through L-R and then when turned join L green to R blue as well as L blue to R green. It's easy enough to do in electronics but I guess no-one makes an electric sized version. Sorry for the floppy CAD, turns out windows paint 3D is ----
A generator cross over switch or a contactor would do what you want.

I don't know how you would switch a 100amp mains using electronics cheaply.

I don't know what you are trying to achieve in your pic, The OPs had his N supply to the meter disconnected, so the meter electronics wouldn't work, as already said a number of times.

Apart from switching colours and Csa it won't do anything to thwart the meter reading.
 
Last edited:
If it was as easy as disconnecting the neutral from the supply of the mainswitch…. And using earth as the return… basically not having anything connected to neutral out of the meter… to stop the meter running…. Everyone would be doing it.

The meters don’t need the neutral to operate… even the old mechanical ones.


Someone comes to read my meter 2 or 3 times a year, even though I fill it in online when asked to.
I’m sure these guys are trained to notice bypasses, strange boxes, smoking nails hammered into the tails….
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Liverpool
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Electrical Engineer (Qualified)

Thread Information

Title
On the fiddle ______________
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
35

Thread Tags

Tags Tags
None

Advert

Thread statistics

Created
Judd,
Last reply from
littlespark,
Replies
35
Views
4,434

Advert

Back
Top