Hi
Been asked to fit just two lights in a small concrete block outbuilding - the building is only 8ft from the house - will be using 1.5 SWA total cable length 30ft - will be direct into a spare way in the CU (RCD additional protection)
My question is do I have to fit a small CU in the outbuilding or can the SWA from the house CU be connected straight to the switch?
Also any recommendations on where to buy Catenary Wire - to to suspend about 8ft between buildings​
terminate SWA into an adaptable box in outbuilding. then use T/E to switch, flex to lights. make sure banjos and fly leads are fitted to the glands. cataenary wire and fixings can be bought as a kit from any reputable wholesaler.
or 10A as it's 1.5mm SWA.
the MCB is to protect the cable. he could also fit a 5A FCU in the outbuilding
Thank you all for your replies, appreciated - will use a 5 or 6 amp mcb and a 3A FCU in the outbuilding - assuming the 3 lights are 100w the full load is only going to be 1.3A.
YOU MAY HAVE A PROBLEM WITH DISCRIMINATION. A 6a mcb WILL PROBABLY OPERATE BEFORE A 3a FUSE. in the case of a lamp blowing.
edit: sorry for the caps. lock was on.
I would be tempted to fit a metal clad FCU and gland the SWA straight into that, then a short length of 20mm plastic up the wall to protect the t&e and clip out to the lights.