I've been asked to quote for a supply and rewire of an outside garage and stable block. I can find nothing oin BS7671 regarding outside garages, though I assume the stable block will come under agricultural use. The plan is to replace the previous property owners cheap and shoddy wiring with a burried SWA cable, fed off the CU RCD protected rail and then a separate breaker box for lighting and power in the garage. This will then feed the garage and stable block. Bulkhead lights and IP55 rated switches and sockets in both garage and stable block. Basicall I want to know if the cableing can be done with twin and earth or whether it neeeds to be in conduit. In BS7671 it states that the protective measure of placing out of reach is not allowed in agricultural areas so rewiring with t/e, even in inaccessible place, is prohibited in the stable but what about the garage?

TIA
 
why don`t you use a 300mA RCD top end (for fire protection)...then give it 30mA bottom end....
 
I've been asked to quote for a supply and rewire of an outside garage and stable block. I can find nothing oin BS7671 regarding outside garages, though I assume the stable block will come under agricultural use. The plan is to replace the previous property owners cheap and shoddy wiring with a burried SWA cable, fed off the CU RCD protected rail and then a separate breaker box for lighting and power in the garage. This will then feed the garage and stable block. Bulkhead lights and IP55 rated switches and sockets in both garage and stable block. Basicall I want to know if the cableing can be done with twin and earth or whether it neeeds to be in conduit. In BS7671 it states that the protective measure of placing out of reach is not allowed in agricultural areas so rewiring with t/e, even in inaccessible place, is prohibited in the stable but what about the garage?

TIA

If that is the initial plan, ..why would you then want to use T&E in the garage section of this outbuilding?? Do a proper job with either PVC conduit or SWA cable throughout the garage and the stable.
 
why don`t you use a 300mA RCD top end (for fire protection)...then give it 30mA bottom end....

You can't rely on a 30mA and a 300mA RCDs having discrimination, the only way to achieve that is with a S type RCD upstream. Then it would be better to use a 100mA S type unit...
 
whatever you do just remember that the average horse can reach about 6 to 7 feet,and board horses love cable and fittings so solid and secure is the way to go.done enough work in stables to know exactly what they can do.
 
In BS7671 it states that the protective measure of placing out of reach is not allowed in agricultural areas so rewiring with t/e, even in inaccessible place, is prohibited in the stable but what about the garage?

"Placing out of reach" only relates to bare conductors, eg live overhead supply cables, and is not relevent here.

Nothing stopping you using twin and earth where appropriate, ie where it's not going to be subject to impact or bitten by animals. phil d's point is a good one; it may be worth considering the use of galvanised metal conduit where horses have access.
 
would metal conduit all of the the rewire because of where it is....any sockets in the stables (if still in use for Horses and not just referred to as the stables because of what they used to be) should be commando type with an additional inbuilt RCD......there are MK ones in Screwfix about £120 each but well justified here.....as ordinary 13 Amp sockets would be open to water/dampness and dust, especially as nowadays a lot of people like to use a pressure washer to clean these types of location regularly....

Garage, I would fit metal clad double/single sockets with inbuilt RCD, again available at wholesalers or Screwfix...
 
You can't rely on a 30mA and a 300mA RCDs having discrimination, the only way to achieve that is with a S type RCD upstream. Then it would be better to use a 100mA S type unit...
yep...should`v known better really..lol...
 
I've got no idea mate, can't stand horses!

With the installation I wouldn't be putting conduit drops in the stable area itself, just in the passage way/corridor to the pens.

I'd use ip rated switches and sockets due to damp conditions and possible spray from cleaning.

Either have one two gang switch for the pen areas and one for corridor, or have each pen switched separately via a switch outside each door.

Don't forget the gaskets on the bezer boxes.
 