Hi everyone.
I went to a small job today for an outside lighting fault. There is a sw feed and neutral coming back from a switch, to a jb. 1.5mm 3 core cable out to the first outside light. No power. 230v at the junction box, good connections. At the 1st light, no voltage... Continuity between cores,all clear. Ins res, starts at 6m ohms and increases upto 30 ish. In theory, the cable should be ok? After doing the ins res test, livened back up and at the 1st light, 170v then slowly drops until about 10v and stays....
Any opinions or similar occurrences?
Thanks, Chris
 
Hi-Chris, just for Clarity are you saying a T&E is joining to a 3 core armoured and you cannot measure voltage at the first light?
 
sure cable isnt nicked somewhere, can still get ok reading untill load is applied then you dont
 
1st outside light is disconnected.
Yes t&e to jb and armoured out. Disconnected armoured at both ends to test to gain ins res readings. Head scratcher
 
The sw feed and neutral is just the other side of the wall comes through to surface trunk and into the jb
 
well if you have meggared the armoured from the JB to the first light then you should know if there is a problem or not Chris.
 
I've mentioned the results I got. There obviously is a problem but the ins res result is higher than 2 and there is no short circuit. Getting 170v for a short while before dropping to nothing seems strange to me. Thanks for the positive feedback though
 
I've mentioned the results I got. There obviously is a problem but the ins res result is higher than 2 and there is no short circuit. Getting 170v for a short while before dropping to nothing seems strange to me. Thanks for the positive feedback though

have you checked for water tracking in the lights or a failing neutral. with a N fault you can have 230v with no load and a lot lower when the smallest load is attached..
 
well I think you haven't measured the cable results correctly, look chris if you have confirmed the armoured is okay to your mind and there is power at the JB and not at the light then really there can be only one result, it is not rocket science is it fella. however do you think 6 ohms is a good reading and not an issue? power at the JB, but no power at the light? and an armoured unbroken between, come on fella, get a grip what do you think?
 
a bad connection somewhere, showjng OK under no load, but as soon as you apply a load, even that of a meter, voltage drops away. could be on the neutral just as well as the line.
 
No load... Completely disconnected. Just the armoured tested then obviously dobbed in to discover voltage was falling but not into light.
 
The armoured goes under a driveway. They have had nothing done to affect it apparently. I thought it is probably a neutral fault but it happens across line and earth aswel. I am replacing the cable as I can't get to it. Thanks for the constructive advice
 