Hi All
Recently came across an interesting situation whereby a client wanted some extra sockets and lights in the garden. The current lights are fed from a spur run in 2.5mm SWA and buried for approx 3m across a lawn to existing installation of two single sockets and some floods in the borders connected as a radial. The thing is the outside socket is connected as part of the ring circuit and the externals spurred off using the 2.5mm SWA. Is this allowable ? Ring main can be any number of sockets as long as area served is no more than 100m2 but looks like client is running small hot tub (4kw) from outside socket which is RCD protected. Concern is loading on that part of the ring. I have suggested it would be better to disconnect spur and join to new SWA run back to the CU and put on separate breaker. Any thoughts ?
Recently came across an interesting situation whereby a client wanted some extra sockets and lights in the garden. The current lights are fed from a spur run in 2.5mm SWA and buried for approx 3m across a lawn to existing installation of two single sockets and some floods in the borders connected as a radial. The thing is the outside socket is connected as part of the ring circuit and the externals spurred off using the 2.5mm SWA. Is this allowable ? Ring main can be any number of sockets as long as area served is no more than 100m2 but looks like client is running small hot tub (4kw) from outside socket which is RCD protected. Concern is loading on that part of the ring. I have suggested it would be better to disconnect spur and join to new SWA run back to the CU and put on separate breaker. Any thoughts ?