Hi All
Recently came across an interesting situation whereby a client wanted some extra sockets and lights in the garden. The current lights are fed from a spur run in 2.5mm SWA and buried for approx 3m across a lawn to existing installation of two single sockets and some floods in the borders connected as a radial. The thing is the outside socket is connected as part of the ring circuit and the externals spurred off using the 2.5mm SWA. Is this allowable ? Ring main can be any number of sockets as long as area served is no more than 100m2 but looks like client is running small hot tub (4kw) from outside socket which is RCD protected. Concern is loading on that part of the ring. I have suggested it would be better to disconnect spur and join to new SWA run back to the CU and put on separate breaker. Any thoughts ?
 
agreed. a 4kW load should be on it's own dedicated circuit. you couls argue some diversity as the 4kW is mainly the heater which will cycle on/off on it's stat, but if I were doing it, min. would be 20A MCB and 2.5mm cable (dependent on installation method).
 
I also agree that's pushing it. Is there currently only the one ring final circuit for the house?
Looking at fault tolerance between circuits would be another consideration as with that lot outside it's only a matter of time before something gets too wet, and it would be better if the internal sockets stayed on (e.g. freezer and especially the telly !)

The 100 sq. m is guidance in appendix 15 btw and even there it is vague, so not written in stone. As you say it's all about loading anyway.
 
OP, can you confirm something.

At first, you say there’s a 2.5 SPUR going outside in SWA….
then later you say the outside socket is part of the ring, with other things spurred off it.

Can you clarify.
 
Hi All
Recently came across an interesting situation whereby a client wanted some extra sockets and lights in the garden. The current lights are fed from a spur run in 2.5mm SWA and buried for approx 3m across a lawn to existing installation of two single sockets and some floods in the borders connected as a radial. The thing is the outside socket is connected as part of the ring circuit and the externals spurred off using the 2.5mm SWA. Is this allowable ? Ring main can be any number of sockets as long as area served is no more than 100m2 but looks like client is running small hot tub (4kw) from outside socket which is RCD protected. Concern is loading on that part of the ring. I have suggested it would be better to disconnect spur and join to new SWA run back to the CU and put on separate breaker. Any thoughts ?
4kw should a DEDICATED CIRCUIT ,DON'T WANT THE RFC tripping every time the hot tub is in use do we?
 
OP, can you confirm something.

At first, you say there’s a 2.5 SPUR going outside in SWA….
then later you say the outside socket is part of the ring, with other things spurred off it.

Can you clarify.
Outside RCD socket is under cover and connected to the house ring, one circuit for upstairs and downstairs off a 32A MCB in board and then lights / sockets etc spurred off unfused from RCD socket. Connections to ring 2.5mm T+E spur run in 2.5mm SWA.
 
Ive done it before where an existing spur (unfused) to external double socket. Customer wanted a second outside socket away from the house. (outside socket back to back with internal socket)

Options were to fuse the spur to outside and make it a radial, or rewire the existing external onto the ring, and spur the new one off it.

Customer opted for second choice... he didnt want another fuse or switch on the wall inside.
 
How long have they had the 4kw tub plugged into the 13A socket? Is there no sign of any heat damage?
 

Reply to Outside Socket in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi. I'm in the process of getting my qualifications and am taking on some small jobs for family to try and get some experience in. Today I was...
Replies
17
Views
781
Ok i may get slated for this one but here goes; A bit of background info first. Its been a while since ive looked at my iee regs, and ive not...
Replies
12
Views
2K
  • Question
Hi there, I’m a new member to the forum and felt like I could do with some additional insight into a fault I came across on a call-out at the...
Replies
6
Views
411
We have a room in the house that was the kitchen. That has been relocated to a different area, so the old kitchen has been sold off and the room...
Replies
2
Views
595
Ok. Can you cut a ring in half, add junction box, then run a spur off it? I thought it had to be from a socket? Mate of mine wanted me to see if...
Replies
3
Views
714

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock