Just wondering if there is a simple table available to show what size cable(s) will fit into oval conduit?
Specifically 2 x 6mm2 T+E cables (induction hob and oven) and 2 x 4mm2 T+E (socket radial)

Oval conduit comes in 13,16,20,25,32 and 38mm sizes. Which of those sizes will fit the 2 x cables for 6mm and 4mm respectively?
I'm not aware of a simple table.

Mostly I'd use 16, 20 and 25mm oval conduit (actually they are the only sizes I keep).
What you can push down a length depends (a) on how long a length, and (b) how straight the cable it.

Cable drawn nicely of the reel will push down conduit a lot easier than kinked and straightened out cable (it never properly straightens). This can make a huge difference.

For 6mm2 T&E, I'd likely use separate 20mm oval conduits, one for each of the two cables, but I'd guess you'd need 32mm oval conduit it you really wanted to put both in one length.

For 4mm2 T&E, you can fit two cables in a 25mm oval conduit, or a single cable in 16mm oval conduit.

Is the oven big & industrial, just wondering why you need 6mm2 cable, most domestic ovens would be wired in 2.5mm2 or 4mm2.

If you are buying conduit yourself, avoid some of the cheap and nastly types (e.g. Screwfix), which are not very robust and easily crack. They are cheap for a reason. I find TLC seem to do a reasonable type.
 
I'm not aware of a simple table.

Mostly I'd use 16, 20 and 25mm oval conduit (actually they are the only sizes I keep).
What you can push down a length depends (a) on how long a length, and (b) how straight the cable it.

Cable drawn nicely of the reel will push down conduit a lot easier than kinked and straightened out cable (it never properly straightens). This can make a huge difference.

For 6mm2 T&E, I'd likely use separate 20mm oval conduits, one for each of the two cables, but I'd guess you'd need 32mm oval conduit it you really wanted to put both in one length.

For 4mm2 T&E, you can fit two cables in a 25mm oval conduit, or a single cable in 16mm oval conduit.

Is the oven big & industrial, just wondering why you need 6mm2 cable, most domestic ovens would be wired in 2.5mm2 or 4mm2.

If you are buying conduit yourself, avoid some of the cheap and nastly types (e.g. Screwfix), which are not very robust and easily crack. They are cheap for a reason. I find TLC seem to do a reasonable type.
Perfect, thank you so much. Exactly what I was looking for. Yes I use TLC for everything. There's one just down the road

Oven wise I will leave the cabling up to the Spark, just interested in the possible at the moment. I'd rather pay extra and oversize with 6mm even if the oven could comfortably be in 4mm. I have tonnes of spares in the consumer unit so it's really just a few pounds more for 4/5m of cable between 4mm and 6mm
 
I'm not aware of a simple table.

Mostly I'd use 16, 20 and 25mm oval conduit (actually they are the only sizes I keep).
What you can push down a length depends (a) on how long a length, and (b) how straight the cable it.

Cable drawn nicely of the reel will push down conduit a lot easier than kinked and straightened out cable (it never properly straightens). This can make a huge difference.

For 6mm2 T&E, I'd likely use separate 20mm oval conduits, one for each of the two cables, but I'd guess you'd need 32mm oval conduit it you really wanted to put both in one length.

For 4mm2 T&E, you can fit two cables in a 25mm oval conduit, or a single cable in 16mm oval conduit.

Is the oven big & industrial, just wondering why you need 6mm2 cable, most domestic ovens would be wired in 2.5mm2 or 4mm2.

If you are buying conduit yourself, avoid some of the cheap and nastly types (e.g. Screwfix), which are not very robust and easily crack. They are cheap for a reason. I find TLC seem to do a reasonable type.
Well done for answering the question 😁
 
myearlierpostgave a size for 2 x 2.5mm; 2 x 6.0mm. always better a bit too big than too small.. at least, that's what'er indoors says.and she knows nowt about electrics except that if i fit it, her appliances work.
 