You are all making it far more complicated than needed.
Total load = 12.3kW
Divide by 230 = 53.5A
Minus the first 10A = 43.5A
43.5A x .3 = 13.05 Add on the 10A = Diversified load of 23.05 Amps.
6mm T+E will be fine, so long as it isnt run in insulation etc.
It would be advisable to have separate switches.
Agree...
As the installation is an existing one, it just doesn't warrant an additional isolation switch. Not sure if i would actually provide 2 isolation switches on a new installation either for a domestic. A single 45A cooker switch connecting the two cooking appliances via a twin connection plate is more than satisfactory...
There is no need for any switches, if it can be isolated at the fuseboard/CU.
Emergency switching is a factor - if the CU is close by, then there may be no need for emergency switching.
Either way, I'd be happier having 2 isolator switches, but, as usual, local conditions have priority on what is installed.
By far the most common emergency, imo, is a chip pan fire - think I would rather turn off on knobs at the front than grope around the flames for a wall switch :)