Engineer54
Just hook the oven and hob up to a dual connection unit from the cooker controller and the job's done!!
So tell me, what's different about a 4 ring hob and a 4 ring cooker, as to whether they will all be on at one time or not?? The fact remains that a 6mm cable on a 30/32A MCB is good for up to 15KW and has been for a good many years. That's what my hob and oven run on at home, and the hob is a 7 something KW induction hob!!
you still can apply some diversity as the hob rings will be kicking in and out on the stats, so not all 4 will be drawing full current at the same time.

agreed. makers say 20A so that's what they consider a minimum. it goes on a 32A with the oven, so let them argue the ---- as to whether the oven wants over the spare 12A. as eng54 has said in 2 million posts. 6mm on 32A will handle any cooking appliances up to 15KW rating.