Hi All,
If you match the I2 value of BS EN circuit breakers to the current carrying capacity of T&E cable a 4.0mm final circuit (referred to generally as a radial) should be protected by a 20amp circuit breaker.
The same theory also means that a 2.5mm T&E ring final circuit should actually protected by a 25amp BS EN circuit breaker!
2.5mm final circuits (referred to as radial) should be protected by 16amp BS EN breakers.
1.5mm - 10amp BS EN circuit breakers.
1.0mm - 6amp BS EN circuit breakers.

Now it makes perfect sense to adopt this thinking for two reasons:
First it is more efficient therefore saving the planet and will prevent overloading of cabling therefore reducing the risk of fires.
Second it will provide work for unemployed electricians.
stop talking like a penis will you..
 
Darkwood - basically we are allowed to multiply the I2 value by a fusing factor when designing circuits for machines with a heavy starting current.
!

Motors have start-up currents typical 6-10times the motor rating the factor you point to would not allow for this this it isn't what the regulation to talking about .....

To try further convince you although im losing the will to live here....

Can we also please remember that your circuit should be designed so small overload for long periods wont occur if they do then increase the ccc, now small overloads for short periods can be expected especially in ring mains and this will not effect the cable as expressed in previous post.
 
Last edited by a moderator:
Our friend david911cockbur, is trying to substantiate a theory of his, based on only 2/3rd's of the facts or relevant information. As Darkwood has pointed out, temperature plays quite a role, behind the theory that relates to circuit CCC cable size and protective device ratings... The value of X 1.45, isn't a figure that's just been pulled out of the air, as a get out of jail card!! lol!!
 
He has quoted BS EN protection (60898, 61009-1or 60947-2) so in this case Iz should not be less than In no factors applied this also applies to Bs 88, and BS 1361.

Ive tried giving him the theory about using other device where a 1.45 factor can be used.

What i struggle to understand is his OP
He states 4mm later on as been 36amps (installation methods applicable) so why hasn't he put 4mm - 32amps????
 
Last edited by a moderator:
Edit.... Sorry, ....needed to change post but no time to do so right now!!
 
Last edited by a moderator:
All very interesting but we are supplying general purpose socket outlets not machines with high starting currents (we do not need to use a fusing factor in our calculations), therefore the maximum current carrying capacity of the cable remains at most 36amps; and you are trying to claim that you are protecting that cable from small overloads of a long duration using a circuit breaker that will not operate below 46amps (according to the BS EN time current characteristics graphs that are used as our guidance).
This leaves you with a possible 10amp overloading of the cable during normal use or during fault conditions, which is potentially wasteful and/or dangerous if left unchecked for a period of time!

It would appear that your over complicated approach is no more than another excuse made by people like you after you have simply copied what was there before without noticing the difference between BS & BS EN breakers.
House bashing certainly was very simple before clever people like you started sticking your noses in and embarressing everybody concerned.
 
Why would you use a 'fusing' factor (1.45) when using circuit breakers?
Fusing factors are for use with 'fuses', if you have a high starting current and a circuit breaker you can use a C or D type.

Come to that why would you think you need to use a factor designed for high starting currents when supplying general purpose socket outlets?
 
To OP --- Appendix 4
The operating current of the protective device must not exceed 1.45 Iz.
Where the protective device is a BS EN 60898 (amongst others) -THIS REQUIREMENT IS SATISFIED BY SELECTING 'Iz' IS NOT LESS THAN 'In'

So i give you a cable designed for its installations methods has a ccc of 36 amps (Iz) then you can use a 32amp mcb (In)
 
Where overload protection is required, is this not satisfied using ......Ib<In<Iz (< = smaller or equall to)........... which also satisfies I2 < 1.45 Iz as I2 = 1.45 In

As far as I'm aware, these fusing factors are also tripping factors and as stated in the Electrical Installation Design Guide Table 4.1 for a BS EN 60898 b,c and D breaker they are ........No trip below 1.13In and trip within 1 Hour at 1.45In..................above 1.13In but below 1.45In the breaker will trip but not in the conventional time of 1hour.....

Is this not correct?
 
I repeat - why would you consider using a fusing factor (in this example 1.45) when supplying general purpose socket outlets that are protected by a circuit breaker?

You ony need to use a fusing factor if your supplying machines with high starting currents when protected by a fuse.
 
I believe the fusing/tripping factors come from standards for overcurrent devices which include fuses and circuit breakers
 
When supplying general purpose socket outlets it is a simple as it can be; your ccc just needs to exceed the I2 value of the circuit breaker.

This way you protect the circuit from small overloads of a log duration.
 
As you said 'house bashing' is easy, you're over complicating things to excuse your mistake.
 
Yep......where Ib<In<Iz (< = smaller or equall to)........... which also satisfies I2 < 1.45 Iz as I2 = 1.45 In


​
 