Hello all,

As a residential electrician from the U.S. volunteering at a hospital in Malawi, I'm new to commercial. We are working to better protect our bank of 6 Victron Quattros (2/phase) by installing these donated Schneider Electric iPRD1 12.5 (3P+N) SPDs on both the input and the output side of the Quattros (since they are bi-directional).

WhatsApp Image 2026-11-19 at 5.30.52 PM.jpeg

From what I can read in the installation literature, these need to be protected by a C80A MCB, or a 160A fuse. Unfortunately, our main switch (pictured below) is well above that limit at 250A.

WhatsApp Image 2026-11-19 at 5.30.52 PM (1).jpeg

Here in Malawi, a 4-pole 80A MCB is very difficult to get (if impossible). However, we do have several of these 63A MCBs (pictured below). My question is if it's fine to use the lower over-current protection, or if I will run into issues in actual practice? Does anyone install a lot of this particular brand/model? What is the typical setup like? Thanks!

WhatsApp Image 2026-11-19 at 5.30.51 PM.jpeg
 