Hello guys and girls I was wondering if you have any advice to give to a meter installer. I’m often worried about over-tightening terminals inside the meter. How easy is it to break the strands on 16mm copper or 25mm? I tighten the terminal until I can’t tighten them anymore. But I’d this right or should I be just tightening until I feel enough resistance? We never used to have this problem with the old meters as they were flat head terminals and you couldn’t get a lot of torque on them. But these Modular screws with plus and minus screw drivers get a lot of torque on them and I’m worried I could damage the strands.
 
Hello guys and girls I was wondering if you have any advice to give to a meter installer. I’m often worried about over-tightening terminals inside the meter. How easy is it to break the strands on 16mm copper or 25mm? I tighten the terminal until I can’t tighten them anymore. But I’d this right or should I be just tightening until I feel enough resistance? We never used to have this problem with the old meters as they were flat head terminals and you couldn’t get a lot of torque on them. But these Modular screws with plus and minus screw drivers get a lot of torque on them and I’m worried I could damage the strands.
Did your employer issue you with instructions an suitable tooling?
 
Meters are usually grub screws with flat bases or slightly oval, this reduces the chances of damaging the conductors, often in connector blocks or even sockets and switches you with find the grub screws are sometimes pointed, this often leads to damage and shearing of conductors in part or full to the unaware.

I see burnt out sockets all the time from terminals and quite often its not loose but simply because the grub has chomped through half the strands or nearly through the solid conductor.
 
Meters are usually grub screws with flat bases or slightly oval, this reduces the chances of damaging the conductors, often in connector blocks or even sockets and switches you with find the grub screws are sometimes pointed, this often leads to damage and shearing of conductors in part or full to the unaware.

I see burnt out sockets all the time from terminals and quite often its not loose but simply because the grub has chomped through half the strands or nearly through the solid conductor.
Interesting never knew this so should be fine with tightness in meters then with them being flat. I’ve pulled cables out before to check damage and they do get very dented under tightening.
 
I'm very surprised you are not trained with and issued a torque driver in your job.
It’s something I’m going to push for in our team meetings because I think a lot of guys myself included are told to go as tight as you can. As that’s better than not tight enough. But a modular screwdriver creates a lot of torque.
 
That is really scary, you guys are trained to fir electrical meters, the device that has the highest current passing through it and have not been given instruction on how tight the terminals should be? the detail should be in the Mi for the meter in question. and I would have thought that a preset torque driver used to tighten the terminals.
 
Tails to meters are more often than not stranded which allows the cores to shuffle and flatten out a bit, usually leaving a grub screw footprint but as long as they are not cut into or playing up the sides of the grub where poor design leaves a gap then you should be fine.

Think about crimping a stranded cable and a solid cable, the crimper used are often different, indented for solid are common and shaped/pressed crimps for stranded.. this account for how the cores behave when crimped, if you use the wrong one for the cable it can cause a bad joint or damaged crimp/cable.
 
I will also add here, regardless whether a torque tool or just judgement has been used, copper - especially stranded can suffer from creep, this is when you have tightened the terminal and over the next few hours or so the copper will naturally creep into any tiny gaps as it is under high pressure, this can lead to a tight terminal become loose on its own but terminal hole design and grub screw play a key role in eliminating this, this is why meter terminals are often circular and the grub is wider than the bore.
 
That is really scary, you guys are trained to fir electrical meters, the device that has the highest current passing through it and have not been given instruction on how tight the terminals should be? the detail should be in the Mi for the meter in question. and I would have thought that a preset torque driver used to tighten the terminals.
Oh I totally agree, especially considering one mans tight is another mans loose or one mans loose is over tight.
 
No torque tools then bunch of idiots, that would be my first option, know wonder there are fires etc.
We only do what we are told/trained to do. I’m not disagreeing I think the training isn’t good enough. You are given 12 weeks training. 16 meter installs as experience then set off on your own. And don’t get me started on gas
 

Reply to Overtightening Meter Terminals in the The Welcome Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock