I live in a block of flats with an external CU for the external (and some internal) circuits, which are 90% lighting with a couple of sockets here and there.
The RCBOs keep tripping on three of the circuits and when they trip they tend to trip other RCBOs at the same time. Before I get an electrician round I want to do a bit of circuit mapping and basic fault finding to make their life a bit easier. Predictably:
  • no circuit diagrams
  • what is written on the CU is a mess and doesn't seem to bear any relation to what is actually on each circuit
  • mods have been made by residents to various circuits who clearly did not have the necessary knowledge
  • there's also a bar heater and a water heater on the circuit which live in a shed externally
  • there's clearly water ingress to a number of badly fitted external lights which have perished gaskets and missing fixing screws
Before I start I wanted to post a picture of the CU just to get any kneejerk comments from the forum - it seems to be a mix of RCBOs and MCBs which I've not seen before. The three circuits that are tripping are marked but I will see what they trip when I start investigating. One trips immediately, the other two after a few seconds.
I'm a keen amateur but not qualified so do have my own megger, budget clamp meter and a lot of experience in construction.
Any initial thoughts on the attached image before I start doing basic investigations? Will start by mapping out the circuits, then inspecting the external lights for obvious faults, then probably get the megger out.
  • Pandoras Box.pdf
First thoughts are I can't see any test buttons on those RCBO's are they covered by your labels, but the most glaring fault is the external sockets off a MCB, dangerous and not in regulation, unless that MCB is powered off one of the RCBO's.
The most common tripping fault is water ingress into external lights/sockets, I would strongly advise getting an electrician in.
Thanks Mike yes the test buttons are covered by the labels - updated image attached. The RCBOs I believe are Lewden 16/30/SP
Just done a quick check and like I say the labelling is a joke. The external socket is actually on the RCBO-protected circuit labeled "Garage Lights R1H".
  • Pandoras Box2.pdf
Reply to Pandora's Box Fault Finding in the UK Electrical Forum area at ElectriciansForums.net
I sorted the fault fairly quickly as it happens but only because I'd come across it once before and at the time a few people said it couldn't...
Hi all, Gone to look at a intermittent ground floor sockets fault today, the RCBO was tripping at random times with no pattern. Nailed down a...
Hi Guys, Had a call out today about an odd issue with a newish Creda DT storage heater. Basically.. Storage heaters were installed in one flat...
In my bathroom there is supplementary bonding of the bath, bath pipework, and basin pipework before it goes into trunking and exits unconnected in...